over sized expansion tank
Dadgineer
Member Posts: 2
I have a 2.5 gallon electric tank water heater that requires an expansion tank, the smallest tank i can find is 25% larger than needed. will the tank essentially be useless or can it still be installed without causing issues with T & P valve or can we lower the pressure in the tank or is there another option we can use to appease the code official requiring an expansion tank.
In fact, it's good. Reduces the pressure variations in the system.Zman said:There is no downside to an oversized tank aside from cost.
Don't change the pressure in the tank from what is recommended in your setup.
And as for appeasing the code enforcement official -- that's not what the tank is for. It's to prevent catastrophic failure of your water heater or plumbing system from over pressure.Br. Jamie, osb
thank you for the input.0
Remember to adjust the air pressure in your new expansion tank to match the water pressure in your water system.
You must do this with no water pressure on the expansion tank bladder0 -
> Just to add to that, if you don't have a pressure gauge, maybe the Water Authority can test your incoming pressure. Then use a compressor, or take it to an air pump at a gas station, and charge the tank to match the water pressure in PSI.0
