I have to "Fonzie" my oil furnace!

smiller
smiller Member Posts: 4
edited May 2017 in Oil Heating
I have a Williamson oil furnace about 15 years old. From the website, it looks like a Centennial High Boy. When called for heat, it's not firing. The Nest thermostats are working, and the control panel is functioning as well.

When this issue occurs - which is intermittent - there is no smell, heat or other indicator. It just doesn't turn on. Initially, I would remedy the situation simply by turning the power off and on - it would immediately fire. This is the power switch on the furnace, itself - not the emergency shut off at the top of the stairs.

The other day, instead of cycling the power, I went to open the unit up to press the reset button or see if I could tell if anything else was amiss. I never got to that point - the act of removing the cover caused the furnace to fire.

This morning, I went downstairs, and all I did was "Fonzie" it - I hit the side of the furnace with my fist and the furnace fired immediately.

I should also note that once the furnace fires, it does not turn off unexpectedly.

Any suggestions on what might be causing this issue?

Thanks!

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Sounds like a simple wiring/connection issue. Simple to repair, once found. I wouldn't let this go on for too long

    There was an error rendering this rich post.

  • Steamhead
    Steamhead Member Posts: 17,710
    smiller said:

    ..... all I did was "Fonzie" it - I hit the side of the furnace with my fist and the furnace fired immediately.

    I was wondering which of Fonzie's methods you were referring to...... >:)

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    ChrisJ
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Steamhead said:


    I was wondering which of Fonzie's methods you were referring to...... >:)

    I'm guessing the banging on the jukebox method

    There was an error rendering this rich post.

  • Big Ed_4
    Big Ed_4 Member Posts: 3,168
    as Steve had mentioned it could be a loose wire or maybe an control ..The way it is acting I would lean to one of two controls .. Yes go over the connections , ...Thinking your unit has the helix type fan and limit with the button or lever that turns on the fan ? With the switch on and off to get it running , I am thinking primary control with the reset ... But only an voltage meter will give us the correct answer

    There was an error rendering this rich post.

  • HVACNUT
    HVACNUT Member Posts: 6,689
    Inside the furnace cabinet, on the right side, is there a fan center control relay? It's where the thermostat wires connect. If so, on top of that there should be a little black relay with 2 wires going to TT on the burner primary. That black relay, if its there is one, is a common spot for failure of N.O. contacts. The "Fonzie effect" usually closes the contacts.
    Have Pinkie Tuscidero come over and take a look.
  • newagedawn
    newagedawn Member Posts: 586
    if its oil fired, its the burner motor, happens alot with burner motors, stumps the inexperienced, got me,..lol, especially if you had to fonzi it, i had 2 this winter same thing, actually fonzied it right in front of the customer,lol
    "The bitter taste of a poor install lasts far longer than the JOY of the lowest price"
  • ChrisJ
    ChrisJ Member Posts: 16,583
    Sounds like the furnace may have jumped the shark.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • HVACNUT
    HVACNUT Member Posts: 6,689
    > @newagedawn said:
    > if its oil fired, its the burner motor, happens alot with burner motors, stumps the inexperienced, got me,..lol, especially if you had to fonzi it, i had 2 this winter same thing, actually fonzied it right in front of the customer,lol

    >>he said he just turned off and on the service switch before he Fonzied it. He didn't hit the reset which would trip if the OB motor was bad.
  • smiller
    smiller Member Posts: 4
    You guys are cracking me up. I'm going to check it out this weekend, and I'll report back. Thanks all!
  • Zman
    Zman Member Posts: 7,611
    The Fonzi move is quite impressive. Chicks dig it!
    Had a chance to pull one off last summer on a commercial switch gear that would not turn on.
    I bet in your case it is a loose connection or a contactor going bad.
    The motor is likely as well.

    Aaay!
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    newagedawn
  • smiller
    smiller Member Posts: 4
    UPDATE: Had the contractor over and he suggested it was a bad relay. Sounds about right to me. Tested, and so far no problems. Now I need to find something else to "Fonzie" to demonstrate my masculinity.
    MilanD
  • smiller
    smiller Member Posts: 4
    ANOTHER UPDATE: It wasn't the relay. There was a loose wire in the gray Honeywell box (the one with the red reset button). It's "great" that we still need the heat in late May here in the northeast.
  • BobC
    BobC Member Posts: 5,521
    The old loose wire trick will get you every time.

    I live a block away from the bay just south of Boston and that NE breeze was making my tomato plants shiver!

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Zman
    Zman Member Posts: 7,611
    smiller said:

    UPDATE: Had the contractor over and he suggested it was a bad relay. Sounds about right to me. Tested, and so far no problems. Now I need to find something else to "Fonzie" to demonstrate my masculinity.

    Electric Motors are often good candidates for the "Fonzie" move.
    A loose car battery terminal is an easy one as well....
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • flat_twin
    flat_twin Member Posts: 354
    Correctomundo!
  • ChrisJ
    ChrisJ Member Posts: 16,583
    Zman said:

    Electric Motors are often good candidates for the "Fonzie" move.
    A loose car battery terminal is an easy one as well....
    Often you can get a bad starter or fuel pump to run by "fonzying" it with a mallet.