I have to "Fonzie" my oil furnace!
smiller
Member Posts: 4
I have a Williamson oil furnace about 15 years old. From the website, it looks like a Centennial High Boy. When called for heat, it's not firing. The Nest thermostats are working, and the control panel is functioning as well.
When this issue occurs - which is intermittent - there is no smell, heat or other indicator. It just doesn't turn on. Initially, I would remedy the situation simply by turning the power off and on - it would immediately fire. This is the power switch on the furnace, itself - not the emergency shut off at the top of the stairs.
The other day, instead of cycling the power, I went to open the unit up to press the reset button or see if I could tell if anything else was amiss. I never got to that point - the act of removing the cover caused the furnace to fire.
This morning, I went downstairs, and all I did was "Fonzie" it - I hit the side of the furnace with my fist and the furnace fired immediately.
I should also note that once the furnace fires, it does not turn off unexpectedly.
Any suggestions on what might be causing this issue?
Thanks!
When this issue occurs - which is intermittent - there is no smell, heat or other indicator. It just doesn't turn on. Initially, I would remedy the situation simply by turning the power off and on - it would immediately fire. This is the power switch on the furnace, itself - not the emergency shut off at the top of the stairs.
The other day, instead of cycling the power, I went to open the unit up to press the reset button or see if I could tell if anything else was amiss. I never got to that point - the act of removing the cover caused the furnace to fire.
This morning, I went downstairs, and all I did was "Fonzie" it - I hit the side of the furnace with my fist and the furnace fired immediately.
I should also note that once the furnace fires, it does not turn off unexpectedly.
Any suggestions on what might be causing this issue?
Thanks!
0
Comments
-
Sounds like a simple wiring/connection issue. Simple to repair, once found. I wouldn't let this go on for too long
There was an error rendering this rich post.
0 -
I was wondering which of Fonzie's methods you were referring to......smiller said:..... all I did was "Fonzie" it - I hit the side of the furnace with my fist and the furnace fired immediately.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
I'm guessing the banging on the jukebox methodSteamhead said:
I was wondering which of Fonzie's methods you were referring to......
There was an error rendering this rich post.
0 -
as Steve had mentioned it could be a loose wire or maybe an control ..The way it is acting I would lean to one of two controls .. Yes go over the connections , ...Thinking your unit has the helix type fan and limit with the button or lever that turns on the fan ? With the switch on and off to get it running , I am thinking primary control with the reset ... But only an voltage meter will give us the correct answer
There was an error rendering this rich post.
0 -
Inside the furnace cabinet, on the right side, is there a fan center control relay? It's where the thermostat wires connect. If so, on top of that there should be a little black relay with 2 wires going to TT on the burner primary. That black relay, if its there is one, is a common spot for failure of N.O. contacts. The "Fonzie effect" usually closes the contacts.
Have Pinkie Tuscidero come over and take a look.0 -
if its oil fired, its the burner motor, happens alot with burner motors, stumps the inexperienced, got me,..lol, especially if you had to fonzi it, i had 2 this winter same thing, actually fonzied it right in front of the customer,lol"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
-
Sounds like the furnace may have jumped the shark.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
> @newagedawn said:
> if its oil fired, its the burner motor, happens alot with burner motors, stumps the inexperienced, got me,..lol, especially if you had to fonzi it, i had 2 this winter same thing, actually fonzied it right in front of the customer,lol
>>he said he just turned off and on the service switch before he Fonzied it. He didn't hit the reset which would trip if the OB motor was bad.0 -
You guys are cracking me up. I'm going to check it out this weekend, and I'll report back. Thanks all!0
-
The Fonzi move is quite impressive. Chicks dig it!
Had a chance to pull one off last summer on a commercial switch gear that would not turn on.
I bet in your case it is a loose connection or a contactor going bad.
The motor is likely as well.
Aaay!"If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
-
ANOTHER UPDATE: It wasn't the relay. There was a loose wire in the gray Honeywell box (the one with the red reset button). It's "great" that we still need the heat in late May here in the northeast.0
-
The old loose wire trick will get you every time.
I live a block away from the bay just south of Boston and that NE breeze was making my tomato plants shiver!
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Electric Motors are often good candidates for the "Fonzie" move.smiller said:UPDATE: Had the contractor over and he suggested it was a bad relay. Sounds about right to me. Tested, and so far no problems. Now I need to find something else to "Fonzie" to demonstrate my masculinity.
A loose car battery terminal is an easy one as well...."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Correctomundo!0
-
Often you can get a bad starter or fuel pump to run by "fonzying" it with a mallet.Zman said:
Electric Motors are often good candidates for the "Fonzie" move.smiller said:UPDATE: Had the contractor over and he suggested it was a bad relay. Sounds about right to me. Tested, and so far no problems. Now I need to find something else to "Fonzie" to demonstrate my masculinity.
A loose car battery terminal is an easy one as well....Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements