Adding a Taco SR501 to a existing SR503
frozen13
frozen13 Member Posts: 5
edited May 2017 in Thermostats and Controls
Have an existing furnace with 3 current zones, two heat zones, and a DHW tank zone all controlled by a Taco SR-503 and Hydrostat Model 3150. I am adding a heating zone in my basement and have a Taco SR-501 I would like to wire in but not positive on how it should be wired into the existing system.
  • Ironman
    Ironman Member Posts: 7,752
    Bob Boan
    frozen13
  • frozen13
    Ironman,
    I assume I wire it like the second page shows as a master and then move the DHW pump to the SR-501 and the SR-503 becomes a slave my 3 zones of heating? I have attached an image as a
    reference.
  • Ironman
    Do you have a cast iron boiler or a mod/con?
    Bob Boan
  • frozen13
    It's a Buderus G115WS/4 which is cast iron.
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,577
    What if anything is powered by C1 on Hydrostat?
    frozen13
  • frozen13
    I will found out tonight, thank you.
  • frozen13
    Nothing is connected to C1. I've attached some images also.