Condensing boilers without outdoor reset
Parachute
Member Posts: 25
Are there any modulating boilers without outdoor reset or where outdoor reset can be disabled? I want a boiler to respond only to the water temps in the buffer tank and calls from thermostats.
Leave the OD sensor off any American made mod/con and it will fire to the high limit setting. Some will give you an error code.
Worst case scenario: attach a resistor to the OD sensor terminals that has the same resistance that the OD sensor would have at 10*.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
I am not a heating contractor, but I have a Weil-McLain Ultra 3 mod-con that comes with outdoor reset. If I did not want outdoor reset, it suffices to leave the outdoor sensor disconnected, and the boiler will run at maximum temperature.
I cannot imagine why you would want to do this. It seems to me I save more fuel due to the outdoor reset than I do from the condensing.0 -
Most mod-con boilers will allow you to do this. The US Boiler Alpine will allow this but we also do not suggest this as it will affect the efficiency and operation of the boiler. We can change the differential above and below separately to assist in what you are doing and use the PID adjustment for changing the fan ramping speed to extend boiler run time.0
Ok I'm not opposed to ODR. I guess the other way to attack this issue would be to disable the internal setpoint in my Triangle Tube boiler. I want the boiler to switch only on the buffer tank calling for heat not the boiler internal setpoint because that thing starts falling as soon as the igniter shuts off. The buffer tank has a much more gradual temperature drop.0
- 121 Chimneys & Flues
- 15.8K Strictly Steam
