Hydronic Mystery Valve
MikeTsu
Member Posts: 2
Hi, I heard some gurgling sounds come from my Hydronic Heating system when it turned on recently and checked to find out the issue. I had recently replaced a pressure relief valve and had some issues isolating it with all the switches so I figured some air must have entered the system. I have been searching for an air bleeding valve for an hour before I stumbled onto this big brass thing on a pipe. It is not labeled or engraved with any markings. Is this the air purge? If it is how do I use it? The boiler set up goes as follows:
Boiler
This Mystery Item
Expansion tank
Baseboard Heaters
Zone Control Valves
Bleeder Valve (Yes, singular for 4 zones. Don't know why they set it up like that)
Inlet for cold water
Watts 9D-M3 dual check backflow preventer
Pressure Reducer
Taco 007 Pump
Boiler
That's the Micro Bubble Resorber or "air purger".
The brass outlet cap should be open about one turn and the device will work automatically, provided that the float is not stuck.
The top half will unscrew to provide access to the float assembly for cleaning or replacement if needed.
Of course, you'll have to relieve the system pressure and drain it to that level if there are no isolation valves.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.-1 -
I'll have to look online to find a manual for the Resorber and figure out how to unscrew the outlet cap. I just tried with a pair of channel locks and applied moderate pressure and it didn't move.0
It's a SpiroVent and you need a pipe wrench.Bob Boan
Make that 2 pipe wrenches...I would recommend0
Bob mentioned disassembly at the middle seam.MikeTsu said:I'll have to look online to find a manual for the Resorber and figure out how to unscrew the outlet cap. I just tried with a pair of channel locks and applied moderate pressure and it didn't move.
That small top vent thread assembly doesn't come apart easily, or allow access to the float.
Living the hydronic dream0