Hydronic Mystery Valve
MikeTsu
MikeTsu Member Posts: 2
edited April 2017 in Oil Heating
Hi, I heard some gurgling sounds come from my Hydronic Heating system when it turned on recently and checked to find out the issue. I had recently replaced a pressure relief valve and had some issues isolating it with all the switches so I figured some air must have entered the system. I have been searching for an air bleeding valve for an hour before I stumbled onto this big brass thing on a pipe. It is not labeled or engraved with any markings. Is this the air purge? If it is how do I use it? The boiler set up goes as follows:
Boiler
This Mystery Item
Expansion tank
Baseboard Heaters
Zone Control Valves
Bleeder Valve (Yes, singular for 4 zones. Don't know why they set it up like that)
Inlet for cold water
Watts 9D-M3 dual check backflow preventer
Pressure Reducer
Taco 007 Pump
Boiler
  • Ironman
    Ironman Member Posts: 7,927
    That's the Micro Bubble Resorber or "air purger".
    The brass outlet cap should be open about one turn and the device will work automatically, provided that the float is not stuck.
    The top half will unscrew to provide access to the float assembly for cleaning or replacement if needed.
    Of course, you'll have to relieve the system pressure and drain it to that level if there are no isolation valves.
    Bob Boan
    MikeTsu
  • MikeTsu
    I'll have to look online to find a manual for the Resorber and figure out how to unscrew the outlet cap. I just tried with a pair of channel locks and applied moderate pressure and it didn't move.
  • Ironman
    It's a SpiroVent and you need a pipe wrench.
    Bob Boan
  • JUGHNE
    JUGHNE Member Posts: 11,603
    Make that 2 pipe wrenches...I would recommend
    hot_rod Member Posts: 27,830
    Bob mentioned disassembly at the middle seam.
    That small top vent thread assembly doesn't come apart easily, or allow access to the float.