HTP MC80 foghorning on low fire; CO, CO2 good
wcs5050
wcs5050 Member Posts: 165
Anyone have any ideas? Burn oscillating on low fire to the point of extinguish. Burner is kept clean with regular service.
  • Zman
    Zman Member Posts: 7,611
    What are the numbers?
    Sometimes you need to be on the high side of the range on both of those numbers to make it quite.
    Albert Einstein
  • happydave
    happydave Member Posts: 79
    Adjust the gas valve
    Alan (California Radiant) Forbes Member Posts: 4,635
    edited February 2017
    I've had the same problem with both a Munchkin and a Lochinvar Knight. Both have good gas pressure and combustion numbers. Both boilers will complain if the flue has negative slope and thus, standing water in the exhaust.
  • Ironman
    Ironman Member Posts: 7,851
    Set co2 to the richest allowed by manufacturer. Remove or enlarge any CSST tubing within 10' of the appliance.
    I know folks don't wanna hear the latter recommendation, but the corrugation in CSST definitely causes harmonic combustion noise. I removed 15' of CSST from an ATMOSEPHERIC boiler last week and replaced it with black iron. It stop the harmonic resonance completely.
    Bob Boan
    ZmanSolid_Fuel_ManMilanD