Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Should I direct pump this boiler...radiant floor with one zone.

2»

Comments

  • nickh1
    nickh1 Member Posts: 17
    Mark, the fact that it is one zone with a very load head was the exact reason I was second guessing the P/S setup.

    It is a farm shop that we repair equipment in as well as store machinery that must run when it's cold outside. I don't leave the house without long underwear Dec-March so a 60 degree temp and uneven floor temps don't really bother me. It is very comfortable to work in with a sweatshirt. If we were to start from scratch, yes I would put more pipe in, but I was in diaper's when the concrete trucks were there.

    There are 9 of each, just a little hard to see.

    It is not a bypass, but rather the top and bottom supply ports are connected as well as the top and bottom return ports. the point I was making was in reference to why I came out the top and back in the bottom. It was simply a matter of using less pipe to connect it and space concerns.

    I second the gauges are cheap. I was more interested in the thermometer's on them then the pressure side.

    I have a condensate pump ordered with a higher cut out because I have to pump it across the ceiling of the building to the drain on the other side of the building. It is currently draining into a 30 gallon drum that I have been emptying daily. It is producing 7-8 gallons a day. I smile when I see that water and when it was 35 degree's outside you couldn't see the exhaust coming out of the vent pipe.
  • Paul48
    Paul48 Member Posts: 4,469
    @Mark Eatherton
    That was a general statement regarding direct pumping. Again.....With everything being proper, it will always be the most efficient way.
    I stand corrected regarding the tube spacing. It was based on the OP's complaint of not enough heat.
  • Gordy
    Gordy Member Posts: 9,546
    nickh1 said:

    No it is not cycling. The ignition counter counts 10x and it still reads 0. The unit has been running for 3 days. It is currently modulating at 52%.



    There is a backup modine heater in the building, so it wasn't completely cold in here, but the floor definitely wasn't warm.

    nickh1 said:

    Mark, the fact that it is one zone with a very load head was the exact reason I was second guessing the P/S setup.

    It is a farm shop that we repair equipment in as well as store machinery that must run when it's cold outside. I don't leave the house without long underwear Dec-March so a 60 degree temp and uneven floor temps don't really bother me. It is very comfortable to work in with a sweatshirt. If we were to start from scratch, yes I would put more pipe in, but I was in diaper's when the concrete trucks were there.

    There are 9 of each, just a little hard to see.

    It is not a bypass, but rather the top and bottom supply ports are connected as well as the top and bottom return ports. the point I was making was in reference to why I came out the top and back in the bottom. It was simply a matter of using less pipe to connect it and space concerns.

    I second the gauges are cheap. I was more interested in the thermometer's on them then the pressure side.

    I have a condensate pump ordered with a higher cut out because I have to pump it across the ceiling of the building to the drain on the other side of the building. It is currently draining into a 30 gallon drum that I have been emptying daily. It is producing 7-8 gallons a day. I smile when I see that water and when it was 35 degree's outside you couldn't see the exhaust coming out of the vent pipe.


    Sounds to me it's purring like a kitten.

    I still see 10, and 9 as Mark pointed out.
    Mark Eatherton
  • Zman
    Zman Member Posts: 7,561
    This post has been an interesting exploration into the nuances of hydronic design. There have been some good points made all the way around.

    I am curious how many of the folks commenting would actually bother to change this system if it was installed in a shop they own? I for one would not. I don't see a significant savings and am reluctant to go around fixing things that are not broken.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    hot_rodSolid_Fuel_Man
  • hot_rod
    hot_rod Member Posts: 22,023
    I agree, let the sleeping dog lie.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Solid_Fuel_ManGordy
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    The engineer in me would want the second circulator as a spare ;)
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
    nickh1Canucker
  • Gordy
    Gordy Member Posts: 9,546
    One last thing though. Htp recommends pumping into the boiler on P/S piped setup. With the PONPC on the system side.

    They also show direct piped setup pumping out of the boiler.

    So I find it hard to believe that this schematic was just left behind from the more restrictive hxers. There is a reason. Thoughts?
  • hot_rod
    hot_rod Member Posts: 22,023

    Gordy said:


    So I find it hard to believe that this schematic was just left behind from the more restrictive hxers. There is a reason. Thoughts?

    You pickup about 15F margin on the boiling point (presuming a DP of 4 psi across the circ).

    Not meaningful IMHO, but you never quite know what goes on inside the HX in localized areas.
    I think that is a big reason the "pumping into" became the requirement on the first, small tube type HXers. You have a very high temperature from the burner flame, very close to the wall of the tube, and a very thin walled HX. The additional ∆P provided by pumping into the boiler buys you more "wiggle" room, to prevent flashing.

    This shows the relationship and how small deposits on the HX from minerals cause the pin holing of HX.




    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Paul48
    Paul48 Member Posts: 4,469
    With the highly restrictive heat exchangers, I always heard they wanted you to pump towards, to avoid pump cavitation.
  • hot_rod
    hot_rod Member Posts: 22,023

    You would think the traditional approach with relatively high flow rates will protect the boiler without issue.

    However, the newest group of 1 GPM mod-cons really give you some pause when you look at those sketches. If a 5 GPM mod-con needs additional margin.........what does it say about a 1 GPM mod-con?

    Time will tell.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,853
    hot rod said:

    You would think the traditional approach with relatively high flow rates will protect the boiler without issue.

    However, the newest group of 1 GPM mod-cons really give you some pause when you look at those sketches. If a 5 GPM mod-con needs additional margin.........what does it say about a 1 GPM mod-con?

    Time will tell.

    Makes one wonder what the Reynolds numbers would be like in this scenario too... :wink:

    As it pertains to absorbing concentrated radiant energy, that design of HXer doesn't have nearly the exposure that the Gianonni's do. There is a potential, but I think it's smaller than the alternative helical heat exchangers. Still makes one wonder...

    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.
  • Gordy
    Gordy Member Posts: 9,546
    edited December 2016
    The question still remains why on P/S ,and why not on direct piped? Would there not be more potential for a higher delta p in a direct piped scenerio verses P/S where in the latter the delta p would be minimal in the primary(boiler loop) due to shorter, and larger less restrictive piping.

    Edit: to compare to the loch KHN 10:1 all drawings show pumping into the boiler direct piped, or p/s all though HX designs are different.