Interpreting the new service tag..why no CO2 ?
Jack M
Jack M Member Posts: 239
edited December 2016 in Oil Heating
Why does the tag read O2 and not CO2 (as it has in the past)? I went with a new service tech for the boiler this year (new management at the old place allows 40 minutes for cleaning/servicing and that's not much time for this old boiler).
The new service tech said "the settings were way off" but I don't know what "way off" could mean or how this happened.
The new tag has a measurement for oxygen, not carbon dioxide. Is there a way to tell the CO2 levels?
New December 2016 tag:
Old last year's 2015 tag:
  • Info here.
    New England SteamWorks
    newenglandsteamworks.com
  • Zman
    Zman Member Posts: 7,609
    Combustion analyses equipment only measures CO and O2. It calculates CO2. I have never understood why manufactures harp on a number that no one is actually measuring.
    Albert Einstein
  • Jack M
    From RI_SteamWorks' chart (below), the new lower 5.9% O2 for 2016 is an improvement over last year's 8.2% O2. The new (2016) CO2 (not measured) would now increase to 11% (roughly) from 10% CO2 in 2015. This might also mean less excess air? Stack temp is up a bit.
  • Zman
    The real question that should be asked is, what is the CO and why is it not being recorded?
    Albert Einstein
  • Jack M
    No, no measure of CO that I can see.
  • STEVEusaPA
    I don't like " -.06, -.01", I think your boiler's heat exchanger is still dirty/plugged, but the next year it looks better if they are negative readings.
    Also, I wonder if the tech is using a wet kit. I see hand written where there should be a printout.
    Would explain the no CO
  • Zman
    It surely went up when he made the O2 go down. Is it still in spec? I would inquire...
    Albert Einstein
  • Jack M
    This is an old low speed (1725 RPM) oil burner. I did notice that the tech had an electronic box (no printout). The heat exchanger was cleaned (he let me take a photo with my phone) , and the smoke pipe was removed and vac'd out (last year's 40 minute service did not include this effort) .
    Steamhead Member Posts: 18,501
    What model is the burner?
    Consulting