Determining Old Boiler BTU
ertbrandon
Member Posts: 2
Hello, our company was sent out to provide an estimate to replace an old "American Radiator and Standard Sanitary Company" Cast Iron Sectional Heating Boiler. I'm assuming it was manufactured between 1948 and 1967 as in the upper right of the placard it says "American-Standard" and on the bottom "American Radiator and Standard Sanitary Company" The only label or Placard on it are the "instructions for shutting off and lighting" I am trying to find the best way to determine the BTU input of the boiler so we can confirm it is sized correctly and so we can spec out the new boiler properly. It has 8 Burner Orifices and 3 Pilots and 9" Draft Hood.
Any Takers?
Any Takers?
Is this steam? If so calculate the EDR of the radiators and use that figure to size the boiler.0
What is the drill size of the orifices on the burners? Give me that and also a picture of the controls especially the gas valve.0
I'm with @Abracadabra -- if it's steam, get the EDR of the radiators and size it that way. If it's hot water, do a heat loss on the building and size it that way. Don't assume that the boiler that's in there is the correct size! They often aren't...Br. Jamie, osb
Its Hydronic. And we want to know the BTU so we can see if it was sized properly in the first place. Unfortunatley I wasn't able to get the orifice size as they did not want me to turn off the boiler. The other pictures of the LWCO and other controls are crappy so here's what I have.
That's hydronic? What about the McDonnell & Miller low-water cutoff mounted on the left side, which is used on steam boilers?All Steamed Up, Inc.
Consulting0 -
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 75 Pipe Deterioration
- 15.6K Strictly Steam