Low loss header set up correctly?
Jason_Talbot
Member Posts: 22
While I'm at it--can someone explain if this low loss header is set up correctly? Seems counter intuitive to me.
Looking at the first image I will explain the configuration:
Bottom right: Primary hot water flow from the boiler
Bottom left: Primary return from the heating circuits (two floors of radiant and a hydro air unit but not the DHW)
Top left: This feeds hot water to the main heating circuits (two floors of radiant and a hydro air unit but not the DHW)
Top right: This returns water back to the boiler
Thanks!
Jason
Thanks!
Jason
Thanks Gennady. According to that manual my LLH is piped completely wrong. What is the impact of such a mistake. Worth correcting?0
It looks completely correct to me. What do you see wrong?Bob Boan
In the schematic supply enters and leaves the top and return is on the bottom. My system has boiler supply enter the bottom and system supply leaving he top. System return enters the bottom and exits the top.0
The supply from the boiler, the hottest water, needs to feed into the top connection. Supply to the distribution also pipes from the opposite top connection.
Piping wise you could flop, but air removal is best at the hottest location, with vent at topBob "hot rod" Rohr
The left hand pipe on the boiler is its supply; the right side is the return.Jason_Talbot said:In the schematic supply enters and leaves the top and return is on the bottom. My system has boiler supply enter the bottom and system supply leaving he top. System return enters the bottom and exits the top.
What boiler are you looking at?
Bob Boan
ok i'm an idiot- thanks. i mixed up main supply and return. didn't realize the circulator pumps were on the returns (intuitively thought they would be on the main supply pipes)0
The pumps belong on the return in that type of setup. They're pumping away from the PONPC.Bob Boan