New Steam boilers - Williamson versus Weil Mclain

I recently had a contractor install a new steam boiler and it works well and appears to follow all best practices I've read about. My question is specific to the boiler itself. I was quoted and expected a weil mclain eg 45 s to be installed. However the contractor installed a Williams GSA 150; I was told the EG 45 was back ordered and would take two weeks. The contractor did not tell me this upfront, I discovered this during the install.
From the little I've read the Williams is marketed as an entry level model, but they appear to be about the same from pictures and I was told they are the same.
I'm looking for advice....are these the same boilers? I'm happy with the install, but not happy I ended up with a entry-level boiler. Am I over-reacting?

Comments

  • I hope he sized the boiler by measuring the EDR of the radiators.
    Usually the advice here is: choose the competent steam pro first, and then go with his recommendation as to boiler selection.--NBC
  • MikeB001
    MikeB001 Member Posts: 14
    Thanks for the reply....yes the radiators were measured and boiler sized accordingly. I'm only curious on thoughts on these two models and/or differences between the two.
  • Fizz
    Fizz Member Posts: 547
    Numerically eveything is the same, from btu input, out put, efficiency, sq ft of steam, gal of water. Overall weight is greater on Williamson. As far as warranty, you can check with installer or your paperwork. Fizz
  • Paul S_3
    Paul S_3 Member Posts: 1,270
    edited November 2016
    I use Williamson mostly.....it seems to be the same boiler and i have no issues with about 95% of my installs.....(knock on wood)....Williamson is significantly less expensive....the only problem i see with most of the contractors when they purchase Williamson is actually the supply house they purchase it from.....a warranty issue can be a nightmare.....im referring to what i see in my area Brooklyn, Queens Staten island etc....in a nutshell, same boiler less expensive i think.....use a reliable and competent installer that will do the right thing then youll have no worries.....where are you located and do you have pics of the installation? I personally think your installer wanted to save $X,XXX.XX on the installation and purchased the Williamson.....they shouldve gave you the boiler that you were quoted
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
    MikeB001ranzerox
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,144
    Williamson and WM are the same boiler, as far as I know. The Williamson block has Weil Mclain stamped on it. I think that the only difference is the jacket and the price.
    Paul S_3MikeB001
  • KC_Jones
    KC_Jones Member Posts: 5,786
    Here's an interesting question for the pros about this. If you quoted a WM and then installed a Williamson that was X amount cheaper to you, would you pass that savings onto the client? Just kind of curious how the contractor handled this with the OP. I would think the customer should have had this saving passed onto them?
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    MikeB001
  • Paul S_3
    Paul S_3 Member Posts: 1,270
    edited November 2016
    He shouldve its significantly less expensive.....especially since he said in the quotation Weil Mclain....then at the installation brought a Williamson.....bad business
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • MikeB001
    MikeB001 Member Posts: 14
    Thanks for all of the feedback so far. I am located in Western Pennsylvania. here are some pictures of the install. It seems correct based on what I've read. Just not sure if it was skimmed and there is no valve there.



  • Paul S_3
    Paul S_3 Member Posts: 1,270
    edited November 2016
    No skim tapping installed....its piped to the MINIMUM requirements of the manufactire
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
    MikeB001
  • MikeB001
    MikeB001 Member Posts: 14
    You mentioned it was piped to the min requirements. What are the other options / enhanced piping? That could have been done other than the skim tapping?
  • Paul S_3
    Paul S_3 Member Posts: 1,270
    edited November 2016
    Drop header......or just use 2 full size risers to a standard header.....this is too slow steam velocity leaving boiler


    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
    ChrisJMikeB001
  • KC_Jones
    KC_Jones Member Posts: 5,786
    Definitely didn't skim it as was stated. I don't like the long horizontal runs on the return piping because it has no provision to flush it out. I can tell you for certain it will accumulate crud in that pipe. This was the first leak I had on my original boiler so I have seen it first hand.

    I'm not convinced it's to minimum spec. The layout may be, but I can't tell the pipe size. The riser and header out of that boiler are supposed to be 2 1/2" minimum, that kind of looks like 2", but the OP would have to measure it. Measure the diameter of that pipe, if it measures 2 3/8" it's 2" pipe and it's wrong.

    The massive height on the riser will probably help with the minimum piping, but if the size is wrong it's still wrong no matter what.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    MikeB001Neild5
  • MikeB001
    MikeB001 Member Posts: 14
    Thanks Paul. The drop or 2 risers would produce dryer steam and result in better efficiency?
  • Koan
    Koan Member Posts: 439
    @Paul S That is beautiful work!
    Paul S_3
  • Paul S_3
    Paul S_3 Member Posts: 1,270
    edited November 2016
    Yes @MikeB001 .....thanks @Koan .....and @KC_Jones is correct
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • MikeB001
    MikeB001 Member Posts: 14
    Thanks; the riser and header are 2 1/2 inch pipe. So I have met min, I think. I will have them add valve and skim it and I will be commenting on the lack of a valve on the return as well. I'm a bit disappointed as I thought I hired a very reputable contractor.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,226
    Your missing a cover on the boiler switch box and you really shouldn't be using romex on the boiler for wiring (sorry, but I am an electrician as well)

    The piping looks pretty good compared to what we usually see (as long as the sizes are correct) and it should work fine even if it is "minimum standards" some here prefer to oversize.

    as far as skimming they should have done that it will most likely not be an option that can be avoided.

    valves or plugs/caps on the returns line for flushing are optional but nice to have

    everything has a cost and labor and material to go with it. all in all looks like you got an ok job
    MikeB001panick007
  • Double D
    Double D Member Posts: 447
    I assume this is a 2 pipe system. That pressuretrol will not keep the pressure low enough. Is there a name on the radiator traps?
  • MikeB001
    MikeB001 Member Posts: 14
    @Double D, this is a 2 pipe system. What are your thoughts on Honeywell pressuretrol? It was adjusted to keep pressure under 1.5 or 2, I think. Most if not all of the radiator traps appear to be original (1930) and are Dunham No 1A and support up to 15lbs. So far most of them appear to function fine.
  • ChrisJ
    ChrisJ Member Posts: 16,210

    Here's my .02.

    A contractor should never change the piece of equipment that was written into the contract without approval of the customer, either through a change order or a new contract. And if there's a price difference, that should be accounted for too.

    He didn't follow the contract he agreed to, whether the boiler is the same or not. Correct?

    In the eyes of the law the boilers are technically different, no?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    Paul S_3
  • MikeB001
    MikeB001 Member Posts: 14
    @Steven Minnich and ChrisJ. I agree with you both....and I'm not happy this happened. I'm still thinking about how I plan to settle up with my contractor.
  • Tinman
    Tinman Member Posts: 2,808
    I'm guessing it will just take a simple conversation between the two of you?
    Steve Minnich
  • ChrisJ
    ChrisJ Member Posts: 16,210

    I'm guessing it will just take a simple conversation between the two of you?

    I understand we're not supposed to discuss pricing, but can anyone tell the Op the general percentage difference between WM and an identical Williamson?

    Right now they're kind of blind in my opinion.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Tinman
    Tinman Member Posts: 2,808
    @ChrisJ - It doesn't matter if its $30 or $300 less. The OP can easily find that out if he's so inclined. He should have been told before the boiler was delivered to the job.
    Steve Minnich
  • Abracadabra
    Abracadabra Member Posts: 1,948
    ChrisJ said:

    I'm guessing it will just take a simple conversation between the two of you?

    I understand we're not supposed to discuss pricing, but can anyone tell the Op the general percentage difference between WM and an identical Williamson?

    Right now they're kind of blind in my opinion.
    Just off the top of my head I'd say the Williamson is about 20% less than the WM
    BobC
  • Double D
    Double D Member Posts: 447
    @MikeB001 The Dunham return system operates at 8oz. Or less. You should be using a vaporstat to control the pressure in the boiler, a Pressuretrol will not keep the pressure low enough for that system. I also don't see a vent on your air trap (behind the boiler, to the left of the window.) Try posting a close up of that float/air trap.
  • BobC
    BobC Member Posts: 5,495
    i have never been bothered by the inaccuracy of vaporstats AS LONG AS THEY COULD TRIP IN THE RANGE I NEED. If it is set to 4oz and trips at 7 oz who cares as I can dial it down to trip where i want it to.

    That is why I have a low pressure gauge next to the vaporstat.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
    Double D
  • MikeB001
    MikeB001 Member Posts: 14
    @Double D
    Here is a close up picture of what is used as the main vent (per my contractor it was left as is..no need to replace with a main vent). I never got a good answer as to what this is and if it should be replaced with something else. Does this mean I have a vapor steam system? If I leave as is...will the boiler be running too long and wasting fuel?



  • Fred
    Fred Member Posts: 8,542
    Looks like it has a vent holes on the top of it. Is that enough?
  • SWEI
    SWEI Member Posts: 7,356
    The famous Dunham ham!
    Sailah
  • Double D
    Double D Member Posts: 447
    You do have a vapor system. I remember @Steamhead saying the original vents are too small. Can you post a picture of the top cover? You're going to need to drop the pressure below the minimum pressure that pressuretrol will do or yes, you will be wasting fuel.
  • MikeB001
    MikeB001 Member Posts: 14
    @Double D Here is a pic of the top cover. What do you think?

  • MikeB001
    MikeB001 Member Posts: 14
    @Double D
    Here is the top cover. What do you think?

  • Double D
    Double D Member Posts: 447
    The threads on that old vent should be 1/2". A Gorton 2 will work in its place. I would say not enough venting with what's there.
    MikeB001