Snow melt
Paul S_3
Member Posts: 1,291
What is the best insulation for this application? What kind have you guys used in the past with good results? Thanks Paul S
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
347-692-4777
ASMHVACNYC.COM
Barrier X5 insulation and vapor barrier all in one3
I just took a quick look at the X5 product.
If you are looking for a product that is easy to install and you only need an R value of 5.3, it looks like it would do the trick.
With a low R value and 12-15 psi rating, it does not look like a good fit for snowmelt systems that see vehicle traffic.
www.2hsc.com/data/uploads/nofp/nofpbarrierflyerx532508-productsheet.pdf"If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
What is up with a dislike for all the comments?
TaylorServing Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
I guess i have fat fingers....i fixed itASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
yes it did....ASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
Ah, that's better, I was worried...Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
Thanks for letting me know. Our developers at Vanilla re-purposed the Dislike button to create a Thanks button for us. A recent update may have messed with the settings. I've disabled it for now and will look into it.delta T said:I think "Thank" turned into "Dislike"
@Erin Holohan HaskellPresident
HeatingHelp.com0 -
Another question guys or @Mark Eatherton ..... im using a couple condensing boilers here .... question is should i be mixing to the slab preferably or straight pipe it like in the pic above since im using condensing boilers (Instead of 1 boiler there will be 2...and a buffer in place of the closely spaced tees)ASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
I agree with Kurt. Straight in and out. No mix needed and your boiler will be as efficient as it can be. I also agree with Zman that 15 psi density is borderline for vehicular traffic.Paul S said:
Also, skip the buffer. Not needed, really won't do any good unless you are micro zoning or something like that..
ME
347-692-4777
ASMHVACNYC.COM
For most applications you would be looking for a closed cell insulation board with a 25 PSI rating. Dow blue board and Owens Corning foamular 250 are common ones.
On jobs with pavers and vehicles, consider going with higher rated product. Concrete does not flex very much so the weight is distributed over a wide area. With pavers, they can move independently, this will focus the weigh on a small area of foam.
I agree that no mixing is needed with condensing boilers. Buffer tanks are also not needed with such a large load.
I would do primary secondary even if you flow rates are similar. When the system comes up from a cold start, the glycol in the tubes will move very slowly. The boiler will be happier if it has steady flow."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
The difference is XPS versus EPS. EPS is the white styrofoam that your coffee cups are made of. XPS is extruded and much more robust. It comes in green, pink, and blue and as previously noted also comes in different densities per square inch.
ME0
- 167 Indoor-Air Quality