Sealing combustion test holes on pvc

Paul_69
Paul_69 Member Posts: 251
what are options for properly sealing combustion test holes on high eff.boilers/furnaces after taking tests in the pvc venting. Seems like most boilers have provisions built in but some do not and condensing furnaces almost never do.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Robert O'Brien
    Robert O'Brien Member Posts: 3,573
    Brass plug will self tap
    To learn more about this professional, click here to visit their ad in Find A Contractor.
    Paul S_3
  • Steve Minnich
    Steve Minnich Member Posts: 2,868
    Before I started using test port tees, I would drill and tap 1/2" holes and then plug them with brass or stainless tapered plugs.
    Steve Minnich
    New England SteamWorks
  • ratio
    ratio Member Posts: 4,023
    Any thoughts about plastic threaded plugs?
  • hot_rod
    hot_rod Member Posts: 25,175
    ratio said:

    Any thoughts about plastic threaded plugs?

    You may need to run a tap in before a plastic plug would thread in.

    I've put a stainless steel hose clamp around the hole. The clamp off a 3" no-hub band works well. Maybe note "test port" with a black sharpie for the next tech.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Paul_69
    Paul_69 Member Posts: 251
    Brass plug will self tap tight enough to seal good?
    Thx
  • delta T
    delta T Member Posts: 884
    I prefer stainless plugs, I've seen too many brass plugs rot away from the condensate.
  • Tim McElwain
    Tim McElwain Member Posts: 4,655
    Stainless steel is best!
  • Paul_69
    Paul_69 Member Posts: 251
    Thx Tim. U need to drill and tsp pvc or will the plug thread in itself
  • Tim McElwain
    Tim McElwain Member Posts: 4,655
    I pre drill the hole and then use the stainless steel bolt to tap the PVC.
  • Paul_69
    Paul_69 Member Posts: 251
    Thx for clearing that up Tim. I think this is the best way. Taking reading of co outside at termination is not as accurate?? What size bolt 1/8?
  • Tim McElwain
    Tim McElwain Member Posts: 4,655
    I use 1/2" as it is easier to work with. I also use a little RTV sealant on the threads.
  • Henry
    Henry Member Posts: 998
    Brass plugs will rot through within 2 years. 3/8 plastic threaded plugs with some pipe dope work.
  • Henry
    Henry Member Posts: 998
    Brass plugs will rot through within 2 years. 3/8 plastic threaded plugs with some pipe dope work.