Oil to gas steam replacement
Dave0176
Dave0176 Member Posts: 1,178
Doing an oil to gas steamer, adding a hot water heater and running new gas line as the house wasn't piped for NG.
The old boiler was piped wrong as usual, no equalizer. The HW coil was starting to leak and filling the boiler up, so replacement was necessary. Gonna go back tomorrow got a few more things to do then fire it up.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
SWEIBrianT1077Tim Potter
  • EzzyT
    EzzyT Member Posts: 1,378
    Beautiful job as always @Dave0176
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Fred
    Fred Member Posts: 8,542
    Wow, Looks Great!
    Steamhead Member Posts: 18,213
    Agreed. Was this a Vapor system?
    Consulting
  • Dave0176
    @Steamhead thanks, no this is just your basic one pipe. For what ever reason the original dead engineer decided on a 2-1/2 main to the first elbow then down to 2", as you see that 1" dry return is basically a drain for the main as they didn't use any eccentric coupling, just a 2-1/2 X 2" elbow.
  • ChrisJ
    ChrisJ Member Posts: 17,074
    EG-35 with the signature Dave Z© equalizer? :)
    Looks fantastic as always.
  • Dave0176
    Lol thanks its just easier to pipe then the double 45s, and I've had no problems at all with it.
  • gennady
    gennady Member Posts: 840
    I would move this below water level
  • Danny Scully
    Danny Scully Member Posts: 1,465
    I've thought the same thing @gennady, but as @Dave0176 said, he's had no issues. I guess the same would be true of a drop header's height.
  • Dave0176
    edited October 2016
    Why? Explain.
    I know you guys have concerns of water sitting in that pipe and hammering, however I've never had an issue.
    To me it's only an aesthetics thing.
  • Danny Scully
    He's suggesting it's not 28" above the waterline I think, although, it's the equalizer...
  • Dave0176
    I guess that DOES bring up a good question, does the header equalizer need to be 28" above the hartford loop? Im thinking not as most of everyone's installations would be wrong.
  • Danny Scully
    edited October 2016
    I think it would be from the waterline, but really, I don't see it being an issue. The equalizer does just as it suggests, it equalizes pressure. So, I would think the equalizer prevents backup of water and forces it through the Hartford loop and back into the boiler.
  • ChrisJ
    edited October 2016
    No.
    I believe 28" is assumed due to the pressure drop down the main and it also assumes something like 2 PSI operating pressure.
    The header doesn't have that pressure drop therefore water isn't going to back up it 28". Your Z equaliZer is above the boiler therefore should never have water in it.
    Dave, he puts the Z in EqualiZer.
    I don't think water ever gets above the turn in the Hartford loop. This is why hammering is a concern there and a close nipple or wye must be used.
  • ChrisJ
    Where is it written that steam and water cannot co-exist in a horizontal pipe?
    Take a look at all your steam mains on a one pipe system. Water in the bottom..........steam in the top. Works fine.
    The only time you have a problem is if you fill the pipe with water and said pipe is in the path of the steam.
    The equalizer has water in it without a doubt and Dave's horizontal pipe has water in it without a doubt. But, the water and steam co-exist without any problem due to the size of the pipe and the limited amount of water in the bottom of the pipe.
    Pretty sure I'm the one that keeps saying this.
  • Dave0176
    Is this better my brothers??
  • Danny Scully
    No! Stand by your morals @Dave0176! :lol:
    ChrisJ
    As long as that horizontal pipe has a slight pitch so water can drain, it should be fine.
    But those 45s sure look cool!
    Consulting
    kcopp
    Jamie Hall Member Posts: 26,850
    I must admit I like the 45s better, but -- there is a very important thing to remember here (and the horizontal would have been OK too!): you only get problems with things like hammer etc. when there is moving air or steam. In the equalizer you have neither one -- just water from the header finding its way home. Any air/steam in there isn't going anywhere -- it can't. Just equalising the pressure...
  • Dave0176
    All done......
    LionA29
  • Dave0176
    Oh and thank you Peter @Sailah those big mouths work as advertised. That main vented FAST..........
    ChrisJSWEISailah
  • Sailah
    Sailah Member Posts: 826
    Great to hear the feedback thanks.
    Peter Owens
    SteamIQ
  • Paul S_3
    Paul S_3 Member Posts: 1,291
    great job @Dave0176
    ASM Mechanical Company
    Located in Staten Island NY
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • OilToGas
    OilToGas Member Posts: 1
    @Dave0176 Thanks again. We love the new setup. Clean, quiet, dry, and warm. I'll be recommending you to anyone I know who needs heating help--and especially if they have steam. Glad we found an expert to do the job. (I told you this before, but the plumber who quoted the job before we met you "sized" the boiler just by looking at our old one. I dug out the old quote just for fun--he wanted to install a Utica PEG150EID with 391 sqft. of steam and 150,000 BTUs. Crazy. I doubt I would have gotten a drop header from him, either!)
    Thank you again!
    @EzzyT Nice to meet you, too, when you stopped by the other day to see Dave.
    Keep up the good work keeping NJ warm guys!
    SailahKC_Jones
    EBEBRATT-Ed Member Posts: 19,625
    Just my opinion, as far as the equalizer goes I prefer the 90s and yeah, I can measure 45s.
    I feel that the horizontal equalizer is fine because it has no flow in it. At least not enough to cause an issue. It's balancing the pressure from supply to return and draining the header which has no condensate once it's hot.
    As long as the horizontal portion is not at or near the water line I think it's fine