Furnace Fan and Limit Controllers
Options
wws
Member Posts: 1
in Gas Heating
Can anyone tells me if the jumper tap has been removed from the Furnace Fan and Limit Controllers unit as the new unit I bought has a brass jumper and has not been remove, I like to match my old unit. Thanks everyone newbie.

0
Comments
-
The jumper allows the two functions of the control to be electrically isolated. Use a multimeter on the continuity or ohms range to check between the two terminals of the old control. Continuity/low resistance indicates the jumper is installed, no continuity/infinite resistance indicates it's removed.0
-
The jumper is in place as I can see it in the photo. What that means is the 120 volts feed to the fan side will also be on the limit side. That can be a problem if the limit side is wired through the secondary (24 volt side). In that case the jumper should be removed.0
-
Were there three wires on the old control, or four?0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 76 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements