Does this look right?
mahoney
mahoney Member Posts: 13
This is in a house a friend of mine is looking at. Doesn't look right to me.
Shouldn't the stem rise off of the top of the boiler?
  • kcopp
    kcopp Member Posts: 4,577
    Some brands of Gas boilers take the supply risers off the side. The ECR models are ones that do that.... Dunkirk, Utica, etc.
  • mahoney
    Thank you.
  • BobC
    BobC Member Posts: 5,523
    That style of boiler is very fussy when it comes to near boiler piping Unless it is the smallest in that boiler series both supply tappings should be used to get proper operation. Does he know the specific boiler model number?
    Bob
    3PSI gauge
  • GreenGene
    GreenGene Member Posts: 290
    Is that a 90 or a T going into the regulator with no drip leg?
  • ChrisJ
    ChrisJ Member Posts: 16,840
    It's a tee without a drip leg.
    Though I do need to ask, why do stoves, clothes dryers etc not require a drip leg but boilers and water heaters do? Are they not the same exact style gas valve?
  • GreenGene
    I think it varies from state to state and most don't require on appliances except if the manufacturer specifies.
    In our case HVAC manufacturers usually do specify them and it's an out if something goes wrong, no drip leg? not our problem the regulator malfunctioned.
    408.2 Drips. Where wet gas exists, a drip shall be provided at
    any point in the line of pipe where condensate could collect. A
    drip shall also be provided at the outlet of the meter and shall be
    installed so as to constitute a trap wherein an accumulation of
    condensate will shut off the flow of gas before the condensate
    will run back into the meter.
    408.3 Location of drips. Drips shall be provided with ready
    access to permit cleaning or emptying. A drip shall not be located
    where the condensate is subject to freezing.
    408.4 Sediment trap. Where a sediment trap is not incorporated
    as part of the gas utilization equipment, a sediment trap
    shall be installed downstream of the equipment shutoff valve as
    close to the inlet of the equipment as practical. The sediment
    trap shall be either a tee fitting with a capped nipple in the bottom
    opening of the run of the tee or other device approved as an
    effective sediment trap. Illuminating appliances, ranges,
    clothes dryers and outdoor grills need not be so equipped.
  • ChrisJ
    I usually find a change of clothes is the best solution to wet gas.
    However, in all seriousness, how does one know when wet gas exists?
    Gordyrick in Alaska
  • JUGHNE
    JUGHNE Member Posts: 11,453
    Perhaps check the drip trap. Over the years I have found one drip trap with water in it. It was in a dairy barn where the piping supply run a fair length in an unheated attic. It was also a country tap off the transmission main rather thru a city utility, don't know if that makes any difference?
  • Tim McElwain
    Tim McElwain Member Posts: 4,656
    Most gas today is dry gas. The closer you are to the oil and gas fields in the south the more likely you are to get condensibles in the gas (so called "Wet Gas").
    Years ago when we had tin meters with leather diaphragms oil was introduced into the gas to insure the flexibility of the leather diaphragms.
    Drips for liquids, sediment traps for solids (rust and scale in old gas systems).
    Because a lot of gas valves on heating equipment are diaphragm valves the likely hood of a piece of sediment getting across the seat and causing a passing gas valve. Most other appliances use different types of valves. That is why sediment traps are needed on heating equipment. The same for most types of water heater controls they also use a neoprene seat susceptible to getting sediment across the seat hence a sediment trap is needed.
    Hope that helps.
    ChrisJGreenGenekcopp
  • SWEI
    SWEI Member Posts: 7,348
    The condensates are worth far more than the gas is these days, so there is even less likelihood of them ending up in the distribution system.
  • ratio
    ratio Member Posts: 4,061
    I dumped a handful of sawdust out of a dirt leg a few years back. It appears that they ran the gas line over to the stove, fitted the dirt leg, then went upstairs & drilled down to extend it up. By the look of it, it was original to the house, 20's-30's.
  • That's a great boiler, I have lots of Utica boilers in, but both steam risers have to be piped into the system, Dan says so in his books also. When piped correctly, these boilers will deliver dry steam, efficiently, comfortably and quickly.
    Thanks, Bob Gagnon
    Steamhead Member Posts: 17,886
    Looks like a PEG-112. According to the latest I&O manual, here:
    http://www.uticaboilers.com/sites/default/files/240009937 PEG-E IOM REV C.pdf
    you can get away with just one riser. I like to make the header 2-1/2" on this size though, to slow the steam down a bit more.
    Consulting