Flue liner question
Double D
Member Posts: 463
in Gas Heating
Is there a problem using an aluminum liner in a tile lined masonry chimney to vent a gas water heater only? The chimney used to vent an oil furnace and gas water heater. The homeowner was told the liner would need to be stainless due to the fact oil residue will deteriorate the aluminum liner.
I would check with the building inspector, he'll probably say if the chimney is cleaned it's ok.
If it's got a lot of residue and can't be cleaned, yeah, aluminum isn't as tough or resilient as S/S, do it once.0 -
Yeah, that was going to be my follow up, most state the warranty is void if the chimney wasn't cleaned first.0
There's an exception for masonry lined chimneys -- if they were built right and are still right. It's pretty rare around here to find that in the field.0
@GreenGene The chimney is clean with only discoloration on the tile.
@ChrisJ Nothing in the instruction for the liner. I suppose I could contact the manufacturer and ask.
@SWEI inspector is only asking for the listed liner to be installed as per manufacturers instructions.
Thank you all for your input.0 -
I would contact the manufacturer.Double D said:@GreenGene The chimney is clean with only discoloration on the tile.
I learned that after watching my chimney guy call whoever they bought liners from and ask questions.
Once you have their approval, you would need to make sure it's ok with local codes.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Good idea. From what I remember, it is an old one. I will run this by the homeowner.0
- 116 Geothermal