Lenox furnace

davezags
Member Posts: 2
in Gas Heating
Have a Lenox pcmu-ld20n133b starts up fine flame comes on runs about 1 minute than everything shuts down. After minute or so starts again as soon as flame comes on within second or 2 everything shuts down. When it shut down the only thing it will do is if I push fan on on limit fan will run nothing else. White Rodgers 50 e-47-070 no flashing lutes either. Any suggestions
0
Comments
-
Clean the flame rod, check and make sure your ground is stable. Once rod is cleaned measure your microamps should be between 2 to 10 normal around 3 to 5.0
-
Thanks for replying. Had a spare new flame rod installed it. Removed grounds sanded reinstalled even removed cleaned screws holding control box to furnace. controller? I don't get no lights except 1 flash when furnace does kick on. No other time.0
-
What are you getting for microamps when it is running? Run a new ground from the flame rod to the gas valve.0
-
That's a Yorkie not a Lennox BTW.0
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 971 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements