Lenox furnace

davezags
Member Posts: 2
in Gas Heating
Have a Lenox pcmu-ld20n133b starts up fine flame comes on runs about 1 minute than everything shuts down. After minute or so starts again as soon as flame comes on within second or 2 everything shuts down. When it shut down the only thing it will do is if I push fan on on limit fan will run nothing else. White Rodgers 50 e-47-070 no flashing lutes either. Any suggestions
0
Comments
-
Clean the flame rod, check and make sure your ground is stable. Once rod is cleaned measure your microamps should be between 2 to 10 normal around 3 to 5.0
-
Thanks for replying. Had a spare new flame rod installed it. Removed grounds sanded reinstalled even removed cleaned screws holding control box to furnace. controller? I don't get no lights except 1 flash when furnace does kick on. No other time.0
-
What are you getting for microamps when it is running? Run a new ground from the flame rod to the gas valve.0
-
That's a Yorkie not a Lennox BTW.0