Eccentric reducing bushings for steam radiators?
I have a customer that's complaining about water hammer on one specific radiator. It's pitched correctly, runout is pitched correctly, no water being trapped in pipes. Upon disconnecting radiator, about 4-5 ounces of water are found inside. The only thing I can think of is to use an eccentric bushing to reduce the amount of water being trapped in the radiator.
She's taken a video of the hammering, there's 3-4 hammers when steam starts to enter radiator and then it's done.
I don't see why you couldn't do it -- but I also would be rather surprised if it fixed the problem. After all, if that were a common situation, it would be just that -- common, and it isn't. There are hundreds if not thousands of systems piped with regular bushings!
For one thing, the velocity of the steam drops so fast when it enters the radiator, that while one could get a nice gurgle (and sometimes do!) it would be a little surprising if one could get enough velocity to get a hammer.
Double check all the piping -- not that I doubt you, but sometimes a little six inch piece can sneak in unnoticed and cause a lot of trouble.Br. Jamie, osb
Yeah... I'm stumped on this one. Spent too much time already trying to figure this out. Never happens when I'm there... sort of like when you take your car to the mechanic.. But she's got the video with sounds of it happening in the middle of the night. I've even thought that she's purposely banging on the radiator herself with a hammer.... dunno..Jamie Hall said:
How large is the radiator? Maybe vent it a little slower. eccentric bushing
or coupling or turn down with a reducing 900 -
You sure it's not expansion noises?
It's an 3 col, 38" 8 section 40edr, vented with a mom#4.EBEBRATT-Ed said:How large is the radiator? Maybe vent it a little slower. eccentric bushing
She says that the hammering has definitely reduced with the new vent, but it still hammers.
Some videos she emailed to prove the hammering, which of course never happens when I'm there.
hammering starts at :50 in, expansion noises before and afterhttps://www.youtube.com/watch?v=9AKhpNztk0w
hammering on this one starts at about 1:00 in for about 1 min, then starts up again at around 2:55https://www.youtube.com/watch?v=jIRxf7t3NtU
Is it possible this is after a set back or after she has just turned the heat back on after having it shut down for a while or after she has shut the valve to this radiator off for a while and just opened it again and that radiator/any water sitting in the bottom has gotten really cool/cold? It sounds more like expansion of or between the sections than actual hammer.0
Hmmm.....Can't see the vent. Maybe the angle.0
Steam collapse? Vapor gets over standing puddle of condensate and collapses in on itself, causing banging? Just the radiator expansion would be enough to wake me up. Maybe try a TRV on that radiator. Grasping here...
ME0 -
All of my radiators hold water, as you said they're bushed down.
You may have mentioned it, but what pressure is the boiler running and what vents are on these radiators?
Also, what valves are on them? I seem to recall some people having issues with smaller valves that don't allow the steam to pass the water very well.
Is there any chance the hammering is actually taking place in the runout below the floor?
Yes, I have been told there is a difference between hot water valves and steam valves. The steam valves are "fatter" and have more room for the condensate to flow past incoming steam.
Hard to tell unless they are side by side.0 -
1-1/2" steam valve. one of the first things i checked.
vent is a MOM#4 boiler is running at max pressure of 14oz. vaporstat controls 2-stage valve on a WM lgb-13 keeps pressure between 6oz-14oz.
the dark video is early morning. yes, there's a couple degree setback. It's not huge, I don't remember the exact details of the setback they have set offhand. the daytime one i think is midday.
I'm grasping too @Mark Eatherton I'm kind of stumped. Got the radiator extremely well pitched, in both front/back and left/right to minimize any condensate sitting in the bottom of the radiator.Mark Eatherton said:Steam collapse? Vapor gets over standing puddle of condensate and collapses in on itself, causing banging? Just the radiator expansion would be enough to wake me up. Maybe try a TRV on that radiator. Grasping here...
ME
I've considered swapping out the radiator with a completely different type just to see if we get anything different. Also as a test, I've even thought about piping the whole thing in 2" down to the stub out of the floor. I'd have to turn the radiator in the other direction though.
@Paul48 , yeah there's a vent on the left. Video is taken from the right so you can't see the vent that's there.Paul48 said:Hmmm.....Can't see the vent. Maybe the angle.
I've pulled the bonnet off and checked the inside of the valve for anything loose that might be trapping water... nothing there
Oh, also, nuts on all the rods were checked for tightness and snugged up a bit.
@Fred there's some expansion noises in the video, but the loud ones are definitely water hammer.0 -
Well I'm out.Abracadabra said:1-1/2" steam valve. one of the first things i checked.
ME
I bolded what I was about to type next until I saw you already did it.
Here's an idea.
Can you please stop finding weird problems that make no sense?
That would be great.
I'm going to have to fall back on, are you 100% sure the hammering is in the radiator and not the runout below it?
LOL.... I can handle the easy ones... it's these freaky weird ones that annoy the crap out of me that I figure others would find interestingChrisJ said:
Here's an idea.
Is there any chance that crud has washed to the center of the bottom of the radiator and created a dam like effect, holding water, on the far side of the radiator, further away from the valve?0
Hmm.. maybe.. I'll add this idea to my to-do list.Fred said:Is there any chance that crud has washed to the center of the bottom of the radiator and created a dam like effect, holding water, on the far side of the radiator, further away from the valve?
Abracadabra, did you make any discoveries in this investigation? I am looking at an almost identical situation and was looking for a similar solution (eccentric reducing bushings), but haven't found such (in the needed size). I would love to hear if you've learned anything since your last post a couple years ago.0
I had one similar to this. I took a vinyl hose and a shopvac to clean out muck damming radiator. The runout had been pitched wrong but was corrected over a year ago. However all that sludge from the years had washed to one side, about 2 sections in.
Cleaning it out did the trick. Haven’t heard anything in over a month.0 -
@Abracadabra, is it a modern 1-1/2 hand valve?0
The original post is two years old.0
Lol thanks @Fred. Guess he figured it out0
Put in a new smaller radiator. No more noises, quiet as a mouse.
I've since installed that radiator for another customer and it too is quiet as can be. Guess the old radiator wanted a move to a different home...0
- 87K THE MAIN WALL
- 116 Chimneys & Flues
- 109 Geothermal
- 991 Plumbing
- 389 Solar