Eccentric reducing bushings for steam radiators?

Has anyone seen the use of eccentric reducing bushings for steam radiators? Just about every radiator I've seen is threaded for 2" and then is bushed down to whatever (1-1/2", 1-1/4", 1") using a regular bushing. This traps water in the radiator.
I have a customer that's complaining about water hammer on one specific radiator. It's pitched correctly, runout is pitched correctly, no water being trapped in pipes. Upon disconnecting radiator, about 4-5 ounces of water are found inside. The only thing I can think of is to use an eccentric bushing to reduce the amount of water being trapped in the radiator.
She's taken a video of the hammering, there's 3-4 hammers when steam starts to enter radiator and then it's done.
I have a customer that's complaining about water hammer on one specific radiator. It's pitched correctly, runout is pitched correctly, no water being trapped in pipes. Upon disconnecting radiator, about 4-5 ounces of water are found inside. The only thing I can think of is to use an eccentric bushing to reduce the amount of water being trapped in the radiator.
She's taken a video of the hammering, there's 3-4 hammers when steam starts to enter radiator and then it's done.
0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 563 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 51 Job Opportunities
- 7 Recall Announcements
Comments
For one thing, the velocity of the steam drops so fast when it enters the radiator, that while one could get a nice gurgle (and sometimes do!) it would be a little surprising if one could get enough velocity to get a hammer.
Double check all the piping -- not that I doubt you, but sometimes a little six inch piece can sneak in unnoticed and cause a lot of trouble.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
or coupling or turn down with a reducing 90
She says that the hammering has definitely reduced with the new vent, but it still hammers.
Some videos she emailed to prove the hammering, which of course never happens when I'm there.
hammering starts at :50 in, expansion noises before and after
hammering on this one starts at about 1:00 in for about 1 min, then starts up again at around 2:55
ME
You may have mentioned it, but what pressure is the boiler running and what vents are on these radiators?
Also, what valves are on them? I seem to recall some people having issues with smaller valves that don't allow the steam to pass the water very well.
Is there any chance the hammering is actually taking place in the runout below the floor?
Hard to tell unless they are side by side.
vent is a MOM#4 boiler is running at max pressure of 14oz. vaporstat controls 2-stage valve on a WM lgb-13 keeps pressure between 6oz-14oz.
the dark video is early morning. yes, there's a couple degree setback. It's not huge, I don't remember the exact details of the setback they have set offhand. the daytime one i think is midday. I'm grasping too @Mark Eatherton I'm kind of stumped. Got the radiator extremely well pitched, in both front/back and left/right to minimize any condensate sitting in the bottom of the radiator.
I've considered swapping out the radiator with a completely different type just to see if we get anything different. Also as a test, I've even thought about piping the whole thing in 2" down to the stub out of the floor. I'd have to turn the radiator in the other direction though. @Paul48 , yeah there's a vent on the left. Video is taken from the right so you can't see the vent that's there.
I've pulled the bonnet off and checked the inside of the valve for anything loose that might be trapping water... nothing there
Oh, also, nuts on all the rods were checked for tightness and snugged up a bit.
@Fred there's some expansion noises in the video, but the loud ones are definitely water hammer.
I bolded what I was about to type next until I saw you already did it.
Here's an idea.
Can you please stop finding weird problems that make no sense?
That would be great.
I'm going to have to fall back on, are you 100% sure the hammering is in the radiator and not the runout below it?
Cleaning it out did the trick. Haven’t heard anything in over a month.
I've since installed that radiator for another customer and it too is quiet as can be. Guess the old radiator wanted a move to a different home...