Thermostat Not Working Properly
Mark1978
Member Posts: 1
in Gas Heating
Thermostat type Honeywell RTH6400 Series.
When I have my program set for the heat to come on to 20 it doesn't come on when the room temp falls below 20. The thermostat reads that the heat is on (as per the pic) but the furnace is definitely not on. What I have to do is manual adjust the requested heat temp below the room temp to turn off the heat on sign (relay) on the thermostat. The thermostat will then click off, I then turn the heat setting back to the desired temp and the furnace comes on without issue but will only raise by 2 degrees and then I manual have to repeat the same thing over.
How's the battery?Br. Jamie, osb
Are sure you have your schedules programmed correctly. The "Temporary" Heat setting will hold the set temperature only until the next scheduled program. The "Heat" sign on the display is only an indication that you have selected the Heating system as opposed to the "Cool" system or one of the other options. Doesn't mean that the furnace should be running at that particular time.0
I have that same thermostat, I notice it says "HEAT ON" in one of your pictures the system should be on at that time. Can you hear the thermostat relay click on? I'd try replacing thae batteries to be sure.
3PSI gauge0 -
What unclejohn said. Whenever the stat says "heat on", the furnace should be running. What happens is that for some reason the furnace doesn't light (or goes out), so the safety control locks out until it's reset, by turning the heat off & back on. It sounds like it's time to call a pro.0
