Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

This little thing may have saved my life today (CO).

Options
I walked into a boiler room for a consultation and this alarm, which I activate every morning and keep clipped to my jacket, sounded within about 20 seconds. I looked at it immediately and it was at 45 parts per million of carbon monoxide and rising fast. I grabbed my client and his assistant and ushered them out of the room without immediate explanation, shut the boiler switch, and looked again at the alarm. By that time it was at 94ppm CO and still rising. A total of about 60 seconds had passed since we entered the boiler room at that point.
As you might expect, I didn't smell a thing, see a problem, or have any reason whatsoever to suspect there was a venting problem of any kind.

I bought this alarm for $150 on Amazon after seeing it clipped to every NYC Boiler Inspector's clothing. It will now be standard equipment for my field techs and myself just as it is for the inspectors.

I've disabled this boiler until the condition can be corrected.

I'm considering this a close call.

Best to all,
John
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
jonny88SWEITinmanSTEVEusaPA4JohnpipeBob Bona_4Jean-David BeyerErin Holohan Haskellkcopp

Comments

  • ChrisJ
    ChrisJ Member Posts: 15,672
    Options
    What caused the problem?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    jonny88
  • Tinman
    Tinman Member Posts: 2,808
    edited November 2015
    Options
    Based on your experience, I just ordered one for me.
    Steve Minnich
    JohnNY
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,506
    Options
    After a huge scare where I ended up in the ER, I carry one into every job. Glad you posted this yourself and not someone else posting a link about your tragic story online
    steve
    TinmanJohnNYSWEIvr608
  • unclejohn
    unclejohn Member Posts: 1,833
    Options
    How do you keep your hands so clean?
    rick in AlaskaBoon
  • JohnNY
    JohnNY Member Posts: 3,230
    edited November 2015
    Options
    No more wrenches, unclejohn.
    Instead, this:
    72°f, LLC


    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    Erin Holohan Haskell
  • 4Johnpipe
    4Johnpipe Member Posts: 480
    Options
    Nice web site @JohnNY
    LANGAN'S PLUMBING & HEATING LLC
    Considerate People, Considerate Service, Consider It Done!
    732-751-1560
    email: langansph@yahoo.com
    www.langansplumbing.com
    TinmanJohnNY
  • Robert O'Connor_12
    Robert O'Connor_12 Member Posts: 728
    Options
    Glad to hear it worked and no one got hurt!
  • GW
    GW Member Posts: 4,692
    Options
    I ordered two today (ma and my service tech).
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    JohnNY
  • delta T
    delta T Member Posts: 884
    Options
    Funny how the world tells you things, I read this post yesterday morning, and then yesterday afternoon I suspect I may have been exposed. Ordering one today, not taking the chance again.

    Customer recently bought the house, complains the furnace turns on and off all time. Found the dip switches on the control board set for 2 stage heat, but no fan speed attached to the lo heat terminal on the board. so....ignition sequence was fine, but then the fan failed to come on. burner would continue until high limit tripped, then burner would shut off and high heat fan stage would come one. after figuring out the problem, I switched the furnace back to single stage heat, and watched the burner fire, and the main blower come on. This caused a huge change in the burnerw flame (pulling out of heat exchanger, going crazy) . Turned it off immeadiately, thought to myself your dumb, had the bottom cabinet door off when the fan kicked on of course its going to affect the burners. closed it up re started the furnace, and nope, still does it, combustion analyzer showed CO of over 1500 ppm in exhaust once the blower kicks on, around 150 with the blower off. heat exchanger is cracked. most likely caused by the way it has been operating for three years since it was installed. The only reason this hasn't hurt or killed anyone is becuase the burner has never been running with the main blower.

    I shut the thing down and it will be replaced.

    I share this because during testing, my combustion analyzer was showing 0 ppm CO if the probe was in the ambient room, or the supply plenum. however after being down there and lighting the furnace a few times for diagnostics, I noticed I started to feel light headed, and got a slight headache, nothing much but enough that I noticed it, and decided I might want to be safer than sorry. shut everything down for a little bit, opened a window and went outside. after about ten minutes I felt better and continued to work. May have been nothing, but at least with one of these I will know long before I feel symptoms.

    Not taking the chance anymore.
    JohnNY
  • Tim McElwain
    Tim McElwain Member Posts: 4,621
    Options
    We talk about personal protective equipment in my classes all the time and we give out data sheets and offer special pricing on several different low level 9 PPM detectors that alarm immediately. If you do not test you do not know. Low level is the only way to go as I have them in three rooms in my house. As also do my children and grandchildren. They make great Christmas gifts.

    Shame on any of you who have been to my classes and don't have one you carry with you all the time.
    TinmanJohnNY
  • NYplumber
    NYplumber Member Posts: 503
    Options
    My Sensit P100 rings when i stand behind vehicles that are running. It makes one think how much CO we are exposed to on a daily basis.
    :NYplumber:
  • aceboiler
    aceboiler Member Posts: 14
    Options
    Wow,good to know someone came up with that.
    I have been gassed a couple of times.
    I figured I needed one intergrated into my watch.
    This one will get ordered for me.
    Glad you had it and no one got hurt!
    JohnNY
  • Answerman
    Answerman Member Posts: 21
    edited February 2016
    Options
    JohnNY said:


    I bought this alarm for $150 on Amazon after seeing it clipped to every NYC Boiler Inspector's clothing. It will now be standard equipment for my field techs and myself just as it is for the inspectors.

    ...

    I'm considering this a close call.

    I couldn't agree more with the importance of always wearing a reliable CO monitor when entering a boiler room, or any space containing combustion equipment. There are two things I'd like to point out, especially to the OP:

    - I recognize the model of CO monitor in your picture, we used to use them at my old company, before I took over managing our equipment and replaced them with better ones. I consider those to be complete junk- We had 3 of them, all about a year old I think (no more than two), and all failed calibration and had various errors. This is not professional or reliable equipment, and for something as critical for your own safety and that of your customers as CO monitors, it's not worth cheaping out.

    There are plenty of good monitors on the market, my favorite and the one I highly recommend are the Drager PAC 5500, which you can find online for a little over $300. I've also used the Testo 317-3, the problem with that one is that it's too easy to hit the mute button or turn it off by accident. The Drager has a loud alarm which can't be turned off, as well as vibration and flashing lights.

    - While 94ppm CO is very serious, and a legitimate emergency situation, you were probably in no immediate danger at that level. While sources and individuals vary, to put that in perspective, it would take several hours of exposure at that level to produce a "light headache". It's certainly better to overreact than under-react when it comes to CO, but I've learned the hard way that some people can get very upset when you're a little imprecise about describing the level of danger, and throw around the term 'life threatening' for levels that aren't quite there (although I think it's fair and prudent to consider any back-drafting situation as potentially life threatening, regardless of the CO level at that moment)..

    Here's some info about CO levels you might find useful. The chart on the left is from the Testo manual that came with one of their combustion analyzers. i don't remember where i found the chart on the right. Since the sources are a bit hazy, I wouldn't fully trust either one as the definitive numbers, but it should give you a ballpark about the level of danger from short term exposure to various CO concentrations.

    (edit: I originally posted that the 3 cheap CO monitors we had were "less than a year old", I meant to say about a year old, I don't remember exactly).
    Energy & Sustainability Engineer
    ChrisJ
  • Answerman
    Answerman Member Posts: 21
    Options
    Here's the highest ambient CO I've ever personally experienced in a boiler room. (Granted, this was a foot or two away from the flue, and I was trying to see how high it could get.. It was lower in other parts of the boiler room, but still easily over 100ppm).

    It's not high enough that I need to worry about running out of the room instantly, I think it's fine to take a few minutes to look around before shutting off the boiler and evacuating, especially since I wasn't alone. But it's certainly not a level that anyone should be spending much time in. This particular CO monitor has an upper limit of 400ppm.

    FYI @delta T , I routinely find boilers with over 2,000ppm, but 0ppm ambient. It's not uncommon, at least not with the large, old, boilers I find in NYC multifamily buildings. It's certainly not good, and I always consider it a potentially hazardous situation (as well as a sign of poor combustion efficiency), but a high CO in the stack will only affect ambient CO if there is also back-drafting.

    Also FYI, a CO sensor calibrated for high levels, as I believe most combustion analyzers are, will be less accurate at low levels, which we tend to be more interested in for ambient levels. So a combustion analyzer is not the proper equipment for measuring ambient levels. One more reason it's better to have a separate, accurate CO monitor and keep it turned on at all times.
    Energy & Sustainability Engineer
  • SWEI
    SWEI Member Posts: 7,356
    Options
    70 PPM (measured ~2 hours after exposure began) had a noticeable effect on me.

    The Sensorcon Inspector (photo above posted by @Stephen Minnich) can be calibrated -- and has a fairly decent UI which prevents unintended silencing or shutoffs.
  • captainco
    captainco Member Posts: 793
    Options
    Most combustion analyzers are plenty good for ambient testing if they have been turned on in the right place. They do zero out ambient CO when you turn them on so if there is 10ppm where you are standing the analyzer will zero that out and not read 1ppm unless there is 11ppm. Only Bacharach can be programmed not to zero. I have used 50ppm, 100ppm and 500ppm cal gas on analyzers and regardless which one you use the others come in right on the numbers.

    The Sensorcom is on of the best I have seen. Not only can it be calibrated it has a replaceable battery which means it can operate for more than two years.

  • JohnNY
    JohnNY Member Posts: 3,230
    edited February 2016
    Options
    I guess I'm just from the Jim Davis school of carbon monoxide and believe that it's bad for you at most any level.

    And I do appreciate the suggestion for a better unit because, truth be told, this is the second one I'm replacing now in two years.

    (edited to add) That said, @Answerman, the units you recommend are too large to be practical in some cases.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    Canucker
  • Larry (from OSHA)
    Larry (from OSHA) Member Posts: 717
    Options
    We have been using these for several years and have no issues with them. Also, I believe Mark Eatherton found that he likes this one.

    http://www.indsci.com/products/single-gas-detectors/t40/

    Larry
  • Answerman
    Answerman Member Posts: 21
    edited February 2016
    Options
    @SWEI, the Drager PAC 5500 units can be recalibrated, but you have to send it in, unless you have enough units that you want to invest in some pricey docking stations, software, and other equipment. But you can replace the battery yourself (which I have yet to have to do).

    @JohnNY, I suppose there are smaller units available, but I like the size of these. I clip them to a pocket or my belt, or sometimes to the outside of my backpack.

    Just last week, I was standing in the hallway of an apartment building, and out of the blue my CO alarm started beeping (loud enough to get the attention of several residents). It showed about 56ppm just for a few seconds before returning to zero, I think because someone opened a door. After checking several apartments, I identified one apartment that consistently had about 16ppm, +/- about 5, resulting from her oven. I advised her to open the windows, shut off the oven, and informed the management that they should have the oven serviced or replaced. She apparently had a functioning CO alarm, but as we know those don't go off until the level gets pretty high..

    Needless to say, the resident was very grateful that I found the potential safety hazard. I've had the alarm go off many times, though I think this was the first time it reached the low alarm threshold (35ppm) outside of a boiler room.. I can't recommend the Drager CO alarms enough.. (I have no affiliation with them, I just appreciate tools that work well)
    Energy & Sustainability Engineer
  • Steamhead
    Steamhead Member Posts: 16,833
    Options
    Answerman said:

    FYI @delta T , I routinely find boilers with over 2,000ppm, but 0ppm ambient. It's not uncommon, at least not with the large, old, boilers I find in NYC multifamily buildings. It's certainly not good, and I always consider it a potentially hazardous situation (as well as a sign of poor combustion efficiency), but a high CO in the stack will only affect ambient CO if there is also back-drafting.

    Which happens if the flue gets blocked or restricted. That's why our company doesn't tolerate such high CO levels. Fortunately, it's pretty easy to get them down with a few adjustments or some cleaning, or both.

    On one particular boiler that was overgassed, causing over 2500 ppm CO, the chimney was also blocked with about 18 inches of crap- including a couple of dead crows. You could smell the aldehydes coming out of the draft hood about 10 seconds after the boiler lit off.

    Oh, and a tech from a different company had told him this was normal. You can't fix stupid.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Answerman
  • ChrisJ
    ChrisJ Member Posts: 15,672
    Options
    Steamhead said:

    Answerman said:

    FYI @delta T , I routinely find boilers with over 2,000ppm, but 0ppm ambient. It's not uncommon, at least not with the large, old, boilers I find in NYC multifamily buildings. It's certainly not good, and I always consider it a potentially hazardous situation (as well as a sign of poor combustion efficiency), but a high CO in the stack will only affect ambient CO if there is also back-drafting.

    Which happens if the flue gets blocked or restricted. That's why our company doesn't tolerate such high CO levels. Fortunately, it's pretty easy to get them down with a few adjustments or some cleaning, or both.

    On one particular boiler that was overgassed, causing over 2500 ppm CO, the chimney was also blocked with about 18 inches of crap- including a couple of dead crows. You could smell the aldehydes coming out of the draft hood about 10 seconds after the boiler lit off.

    Oh, and a tech from a different company had told him this was normal. You can't fix stupid.
    Jstar wouldn't allow over 55ppm on my boiler. I even tried to get him to go closer to 100, he wouldn't do it. Now it's likely close to 0 because I put everything back to stock, I didn't like the extra steam pressure. I was running close to 1" ! :open_mouth:
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment