l8148j aquastat trouble
 
            
                
                    pjc9906                
                
                    Member Posts: 2                
            
                        
            
                    i just installed an l8148j aquastat. everything is running fine but the burner keeps running, wont shut off. were did i go wrong                
                0                
            Comments
- 
            Is the Thermostat wire... touching?? when you put on T-T make sure it's not touching or that will cause this0
- 
            Do you have a 24 volt gas valve or a powerpile self generating valve?
 If you have a 24 volt valve wire valve to B1 and B3 and insert jumper between TP and Z.
 If you have a powerpile valve wire B1 and B2 to powerpile valve and no jumper between TP and Z.
 Give us the number of the gas valve and the make?
 I had posted this in the other section you inquired in.0