l8148j aquastat trouble
Options
pjc9906
Member Posts: 2
i just installed an l8148j aquastat. everything is running fine but the burner keeps running, wont shut off. were did i go wrong
0
Comments
-
Is the Thermostat wire... touching?? when you put on T-T make sure it's not touching or that will cause this0
-
Do you have a 24 volt gas valve or a powerpile self generating valve?
If you have a 24 volt valve wire valve to B1 and B3 and insert jumper between TP and Z.
If you have a powerpile valve wire B1 and B2 to powerpile valve and no jumper between TP and Z.
Give us the number of the gas valve and the make?
I had posted this in the other section you inquired in.0