Any reason NOT to drop one pipe size coming out of Burnham boiler?
Lordniacin
Member Posts: 13
Looking at piping a Burnham 204, about 80K output.
The pipe connections that come out are 1-1/4". If I pipe around the boiler at this diameter, at my expected boiler flow rate of 8GPM that is a water speed of only 2fps, at the very bottom of the recommended range. If instead I pipe around the boiler with 1" pipe, the water speed becomes 3.2fps, right near the middle of the range.
So, is there any reason I should not come out of the boiler at 1-1/4", immediately go through a reducing fitting down to 1", and continue my near-boiler piping using 1" pipe?
Sorry for the newbie question!
Technically 1" pipe only delivers 72K at recommended flow rates. So your screwing yourself out of 8K0
You will also increase piping heat loss unless you insulate . Short Fat headers are recommended for a reason .You didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
Rich McGrath 732-581-38331 -
If you are building a header, I agree that 1 1/4" is a better plan. If you are just talking about piping to move some BTU's around, 1" will work perfectly.Lordniacin said:Looking at piping a Burnham 204, about 80K output.
The sections with the tappings are used for boiler sizes up to 212k input. Sizing down on your boiler should work just fine."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Yes Zman that is exactly right. I am just talking about using 1" in the part between the boiler and the header, which will be bigger.
Just trying to pick the pipe sizes to keep my flow speeds between 2 and 4fps according to the GPMs in the various parts of the system.0 -
8 GPM would be 3.2 ft per sec in 1" pipe as you correctly calculated. A conservative design would limit you to 4ft/sec."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0
- 87K THE MAIN WALL