triangle tube prestige solo 110 boiler
john_117
john_117 Member Posts: 15
We have replaced the draft inducers twice in the last 9 years for this boiler. The inducer has fallen apart on both.
anybody see this before?
  • john_117
    sorry the inducer wheel has fallen apart
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,589
    Usually cross contamination
    kcoppSWEIZman
  • Bob Bona_4
    You mean like this? Solo 175 day before Thanksgiving. What Robert said, or a fluke. Not common.
  • ced48
    ced48 Member Posts: 469
    Does your system cycle on and off a lot?
  • kcopp
    kcopp Member Posts: 4,670
    Lets see a picture(s) of the outside where your vent and intake terminate....
  • kcopp
    No pix?
    We would love to help...
    kcopp
  • mstrbill
    mstrbill Member Posts: 37
    Mine did the same after 4 years ,just blew apart today , however it does cycle often due to how it is hooked up to a brazed plate hot water heater for domestic and a flow switch , sooooooooooo, i will make changes on my end but TT should use SS for the inducer wouldyathink???
  • kcopp
    Its a whole lot harder & $$$ to make and balance a SS fan blade vs. a plastic one.
    SWEI
  • mstrbill
    TT boasts about their SS , all of it . the plastic one is more like a sugar wafer , what a piece of #^#^^. for a 3700 $ heater , i disagree with the cost benifits . they even sell the repair kit with a briefcase omg. for 1700 $ with more plastic . so until they improve i will not install anymore solos , just soyano.
  • Zman
    Zman Member Posts: 7,611
    Do you have pictures of your terminations?
    Cross contamination is usually the culprit not the plastic.
    Albert Einstein
    kcoppBob Bona_4margsuarez
  • Aaron_in_Maine
    Aaron_in_Maine Member Posts: 315
    edited February 2016
    If the venting is correct you usually don't have a problem. I have solos out there that are 5+ years old without a single issue. I never use a concentric vent no matter what. I would rather use indoor combustion air before a concentric I just don't trust them.
    Robert O'Brienkcopp