Tuning gas valve on aging modcon to revitalize factory AFUE
wcs5050
Member Posts: 177
Does anyone know what happens in the gas valve that throws off factory AFUE? I had my combustion analyzer on a WM series 2 Ultra today. Ox2, CO2, CO were all in range that manual indicated, but AFUE was 89%, as opposed to 92%(still not impressive, but decent for an older offering). Any way to cheat this back? Which way would the O2,CO2 go within the mandated range to raise AFUE. I've heard that gas valves on mod/cons need adjusting after a certain amount of years.
what were the numbers?0
What were the water temps at the time of the test?0
I wonder if this is why my numbers are so improved. I've recently thought my boilers may not be getting the rated btus.njtommy said:Not to mention your firing rate and water temp will change the efficiency numbers.
But 89% is not bad at all.
Have to look at my job notes for levels. Low fire water temp was about 105, high fire about 150.0
Your combustion analyzer gives you combustion efficiency which will always be less than AFUE as they are two different things. Typically combustion efficiency is 8 to 10% less than the advertised AFUE. At best as someone else stated efficiency with the analyzer is a calculated reading not pure from a sensor such as O2 and CO along with net stack temperature. That along with draft are the important numbers.
It is not a good idea to adjust Mod/Cons different than what the manufacturers specs call for.1 -
Lochinvar indicates otherwise in regards to KBN500 gas valve adjustment, years in. Im not talking about tweaking outside range called for. Wondering how to get back to optimum. I realize combustion eff and unit eff are separate, yet proportional.0
Thx zman. That's what I was looking for.0
If that 89% you saw was at high fire, and the 150°F was either a return temp or a supply temp with a small ΔT, it looks about right.0
- 50 Industry Classes
