I'm looking for some help. The city wants me to reduce the PSI's on the 'pressure relief' valve of my GB 142-30, significantly. The GC who built the building and i agree, that for a 63' tall building, with a straight run of pipe, the Penthouse apartment radiators would not work properly with a reduction in the PSI valve. Does anyone have any hard facts about the correlation between PSI's and building height?
  • SWEI
    SWEI Member Posts: 7,342
    The height that actually matters is measured from the circulator to the highest point in the system (often a radiator.) The recommended static charge pressure of the system would be that height (in feet) divided by 2.31 and then add 4-5 pounds.
    If that number comes out above 30 PSI (which it may well for your building) then the boiler must be rated for more than a 30# relief valve.
    Steve MinnichRobG
  • lchmb
    lchmb Member Posts: 2,997
    What is it now and what do they want you to drop it to?
  • Rich_49
    Rich_49 Member Posts: 2,783
    edited November 2015
    The max pressure rating for a GB142 is 44 PSI . Considering a 63 foot height is accurate + 5# you'll need a cold fill pressure of 32.3 # . This height should only be from , as Swei stated the elevation of boiler / circ to the highest radiation .
    The max pressure for the boiler can be found on page 7 of the IOM that came with the boiler . Watts 174A - M3 set for 36# should get you there but I don't think that is your problem . You probably already have a sufficient relief valve and just have an inspector problem . There is probably a code in place that also states that the ENTIRE building must be able to be heated . Ask him how he proposes you accomplish that feat without the required pressure . Thats all far fetched though , maybe he just needs to see the manufacturers specs for the equipment and that 44# is acceptable .
    http://media.wattswater.com/ES-174A-740.pdf
    http://www.bosch-climate.us/files/GB142_IM_72150200_2013_US.pdf
    732-751-1560
    Rich McGrath 732-581-3833
  • caulksoaker
    caulksoaker Member Posts: 3
    I currently have a 50 PSI Relief Valve in place and the 'Inspector' wants a 40, eventhough the Buderus spec sheet says 43.8 or some such. Here's a question...how many increments of Relief Valves are there? Do they drop by 2 PSI's or 5 or 10?
  • Rich_49
    The inspector is right . A 50# valve certainly does not meet the criteria for that boiler and would allow the boiler to exceed max pressure by 6# , no good my friend . Quite simply put , 50# is greater than 44# . A 40# valve set is sufficient for your install based on what you have offered us . Make sure the expansion tank is charged to the cold fill pressure PRIOR to re filling
    732-751-1560
  • caulksoaker
    hmmm. interesting. where do you guys purchase these valves for Buderus? can i just call 'Apollo' and get one for 40 PSI?
  • SWEI
    McDonnell & Miller and Watts both have 40 PSI options. Probably others as well.
  • Zman
    Zman Member Posts: 7,609
    The other thing the inspector will likely be looking at is that the Btu rating on the valve exceeds the rating on the boiler.