Buderus GB 142-30

I'm looking for some help. The city wants me to reduce the PSI's on the 'pressure relief' valve of my GB 142-30, significantly. The GC who built the building and i agree, that for a 63' tall building, with a straight run of pipe, the Penthouse apartment radiators would not work properly with a reduction in the PSI valve. Does anyone have any hard facts about the correlation between PSI's and building height?

Comments

  • SWEI
    SWEI Member Posts: 7,356
    The height that actually matters is measured from the circulator to the highest point in the system (often a radiator.) The recommended static charge pressure of the system would be that height (in feet) divided by 2.31 and then add 4-5 pounds.

    If that number comes out above 30 PSI (which it may well for your building) then the boiler must be rated for more than a 30# relief valve.
    TinmanRobG
  • lchmb
    lchmb Member Posts: 2,997
    What is it now and what do they want you to drop it to?
  • Rich_49
    Rich_49 Member Posts: 2,769
    edited November 2015
    The max pressure rating for a GB142 is 44 PSI . Considering a 63 foot height is accurate + 5# you'll need a cold fill pressure of 32.3 # . This height should only be from , as Swei stated the elevation of boiler / circ to the highest radiation .

    The max pressure for the boiler can be found on page 7 of the IOM that came with the boiler . Watts 174A - M3 set for 36# should get you there but I don't think that is your problem . You probably already have a sufficient relief valve and just have an inspector problem . There is probably a code in place that also states that the ENTIRE building must be able to be heated . Ask him how he proposes you accomplish that feat without the required pressure . Thats all far fetched though , maybe he just needs to see the manufacturers specs for the equipment and that 44# is acceptable .

    http://media.wattswater.com/ES-174A-740.pdf

    http://www.bosch-climate.us/files/GB142_IM_72150200_2013_US.pdf
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • caulksoaker
    caulksoaker Member Posts: 3
    I currently have a 50 PSI Relief Valve in place and the 'Inspector' wants a 40, eventhough the Buderus spec sheet says 43.8 or some such. Here's a question...how many increments of Relief Valves are there? Do they drop by 2 PSI's or 5 or 10?
  • Rich_49
    Rich_49 Member Posts: 2,769
    The inspector is right . A 50# valve certainly does not meet the criteria for that boiler and would allow the boiler to exceed max pressure by 6# , no good my friend . Quite simply put , 50# is greater than 44# . A 40# valve set is sufficient for your install based on what you have offered us . Make sure the expansion tank is charged to the cold fill pressure PRIOR to re filling
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • caulksoaker
    caulksoaker Member Posts: 3
    hmmm. interesting. where do you guys purchase these valves for Buderus? can i just call 'Apollo' and get one for 40 PSI?
  • SWEI
    SWEI Member Posts: 7,356
    McDonnell & Miller and Watts both have 40 PSI options. Probably others as well.
  • Zman
    Zman Member Posts: 7,611
    The other thing the inspector will likely be looking at is that the Btu rating on the valve exceeds the rating on the boiler.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein