Replacement Steam Boiler
67" inches isn't too bad Weil McLain and Peerless boilers are around 32" in height. You run your risers as high as possible then drop as low as you need into a drop header as long as you stay above the top of the boiler. Well I just realized that you have a large system, but even a Weil McLain 80 series is 47" at the top with a 32" water line, you can still use a drop header.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......1 -
Burnham 5 series water level is 30". I need to pour a pad for the boiler, as the floor is in bad shape and basement has water issues so add 4" for slab so thats 34" water line now add 24" to bottom of header plus a 6" header I am at 65" to top of header not leaving only 2" to tie in off the top of the header.0
As Dave said you need to do a drop header. Look at the picture on my profile. That is a dropped header. Risers go up then back down into header. This is a common method used when there isn't much headroom.0
And be very cautious about lowering the water line from the existing installation. You must NOT change that water line either up or down more than an inch or two -- or be prepared to do some significant troubleshooting and repiping of lines out in the system, to maintain proper water seal elevations.Br. Jamie, osb
Thanks KC. Is your drop header 24" above the NWL or it doesnt matter due to the risers being so high out of the boiler??0
The header position on a drop header isn't critical, other than staying above the top of the boiler. Go up as high as you can with riser then back down as far as you need to make the main connections.0
Jamie,Jamie Hall said:And be very cautious about lowering the water line from the existing installation. You must NOT change that water line either up or down more than an inch or two -- or be prepared to do some significant troubleshooting and repiping of lines out in the system, to maintain proper water seal elevations.
I'm not sure I agree with this statement. Many systems, including mine would have no issue with this. I could lower my water level as much as I want and raise it a good foot before I'd be concerned.
I have to think it depends greatly on the system and anyone replacing a steam boiler needs to evaluate the entire system to see if it's a problem.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Well, at least the wet returns need to stay wet.Two-pipe Trane vaporvacuum system; 1466 edr
Only dropping the water line by 3-4". Wet returns. 1 pipe steam.
KC thanks. The boiler risers should come up as high as I can but stay below my distribution piping correct? That will give me about 2' pieces out of the boiler and about 38" above NWL.0 -
As a more general statement, you are right . There are many systems where it doesn't matter at all. There are other systems, though, where the wet returns may rise quite a bit as they go out in the system, and where lowering the water line may just allow the ends to dry. If there is supposed to be a water seal out there, and one dries it out... trouble.ChrisJ said:
I think I use that statement as a good general rule -- to which there are always exceptions but which can be evaluated by someone who really knows what they are doing!Br. Jamie, osb
You saying it, and me commenting on it likely will make the OP consider it as well as many others down the road.
That's a good thing.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1
- 109 Chimneys & Flues
- 973 Plumbing
- 386 Solar
- 17 Recall Announcements