Do headers ever loop or "U?"
We've all seen the basic setup of a header: boiler riser, boiler riser, system riser, system riser, equalizer. Every pic I've seen here has that done in a straight line.
I'm hoping to have my near boiler piping redone soon. My boiler has side tappings (Utica) but an earlier boiler was likely "headerless" with two large three inch mains now located behind and in between the boiler risers. The hartford loop's on the right so that means the boiler risers should connect on the left side of the header. There's a wall on that side, so things can get a little tight. Can you maintain the prescribed order but do it in a U or L shaped configuration?
Steaming along slowly in Wharton, Morris County, NJ.
  • Fred
    Fred Member Posts: 8,542
    Many have done headers in an L shape. That isn't a problem as long as you keep the risers out of the boiler at one end of the Header, followed by the risers to the main, followed by the equalizer at the other end. I can't say I've ever seen a U shaped Header, I'm not sure why that would be necessary even.
  • ChrisJ
    ChrisJ Member Posts: 17,068
    Is mine in what you're referring to as "L" shaped?
    If so then yes, that works fine. A U shape may work too as long as it's pitched continuously towards the equalizer.
  • hvacfreak2
    hvacfreak2 Member Posts: 500
    I was wondering about that also , pretty rad CJ.
    hvacfreak
    Mechanical Enthusiast
    Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV's
    Easyio FG20 Controller
    ChrisJ
  • SteamedInWharton
    SteamedInWharton Member Posts: 62
    @ChrisJ, I'd say that looks like an "L" :smiley:
    ChrisJ
  • KC_Jones
    KC_Jones Member Posts: 5,907
    I think it's a matter of preference and field conditions that can dictate header design. I don't think many will argue straight is the most straight forward design. Chris and I both did an L shape and if you look it was mainly a function of existing conditions and matching up with piping. Mine was the same way. I can't think of a reason a U shaped header wouldn't work as long as the pitch is correct. I think in that situation though I would try something else first. I can't quite get my brain around having 2 parallel pipes in the header and not being able to work it out with just a single pipe.
    2014 Weil Mclain EG-40
    Jamie Hall Member Posts: 26,833
    As folks are saying -- keep the pitches good. However, if you can... just sayin', here... it might be better to go up one pipe size, at least for the U configuration, as there is bound to be some loss and turbulence in the bends.
    vaporvac
    Steamhead Member Posts: 18,197
    Consulting
    KC_Jonesvaporvac
  • SteamedInWharton
    Outstanding @Steamhead
  • dennis53
    dennis53 Member Posts: 64
    If you have 2 or more system risers, make sure they do not have a 90 between them. The slight pressure loss and turbulence due to the 90 can upset steam flow to the last risers.
    Dennis
    vaporvac