monoflo baseboard system
john_117
john_117 Member Posts: 15
replaced the boiler for a small two story house, that has a monoflow tee system with baseboard,purged the system all the rooms heat except one on the second floor.
we've purged the baseboard, even installed a ball valve on the second floor baseboard to purge from the supply and the return. replaced the 007ifc with a 0012ifc to overcome the pressure drop of the monoflow tees, still no flow thru that one baseboard.
  • Paul48
    Paul48 Member Posts: 4,469
    I'll ask the stupid question..........Did someone use regular tees for that baseboard?
  • billtwocase
    billtwocase Member Posts: 2,384
    broken 1/4 turn shut off? How far apart are monoflow Tees?
  • jonny88
    jonny88 Member Posts: 1,139
    gets a little tricky with baseboard on a monoflow.what happened when you bled the rad.Any hot water.If so it aint an air problem as they say.You could cut in 2 monoflow tees instead of one but it might have an impact on rest of system.Check out systems on the toolbar you will get good info
  • j a_2
    j a_2 Member Posts: 1,804
    Did it heat before, the install? And was any rework done on the original system?
  • john_117
    no one monoflow on the supply riser regular tee on the return.
  • john_117
    Thanks all for the input, to solve this we removed the old monoflo tee installed two new monoflo tees the width of the baseboard which orignially was 12". installed a purge station on the supply and return risers. filled and purged, system now operating.
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,584
    A full port ball valve in between the two tees makes purging easy.
    GordySWEIRich_49Zman