Rigid Insulation in Boiler Room

Options
I am insulating my basement with rigid polystyrene insulation. Can i use this in my boiler room? Behind my boiler? Should it be foil backed rigid insulation?

Comments

  • Zman
    Zman Posts: 7,614
    It depends which code you are under the jurisdiction of.
    The bottom line is, no you should not have foam insulation exposed in a boiler room. It has to do with the flame spread rating. It is ok if it is covered with type X drywall.
    "If you can't explain it simply, you don't understand it well enough"