One pipe fuel line looks like 2 pipe

STEVEusaPA
STEVEusaPA Member Posts: 6,506
Saw this today on a new customers ridiculously oversized boiler--Burnham V908 with a Beckett CR1400, on a 13000 sq ft. garage
Was wondering why the manufacturer recommends this? If it were the best way, why not do them all like this?
steve

Comments

  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    It's called a cheater loop. Old school. I've seen them on rare occasions, the granddaddy of the Tiger Loop. I can't remember why they aren't used much. Firedragon would likely know.
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,506
    Thanks for the response Bob.
    I actually did something crazy....download the manual. It apparently relieves pressure on the pump seal when switching from hi fire to lo fire.
    steve
    Bob Bona_4
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    Interesting! I've not been exposed to much commercial burners. I can see that though
  • OuterCapeOilguy
    OuterCapeOilguy Member Posts: 46
    I've not run into that setup yet. The commercial setups I've worked on are all two-pipe. I'd be inclined to replace that loop with a deaerator.