One pipe fuel line looks like 2 pipe

STEVEusaPA
STEVEusaPA Member Posts: 6,505
Saw this today on a new customers ridiculously oversized boiler--Burnham V908 with a Beckett CR1400, on a 13000 sq ft. garage
Was wondering why the manufacturer recommends this? If it were the best way, why not do them all like this?

There was an error rendering this rich post.

Comments

  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    It's called a cheater loop. Old school. I've seen them on rare occasions, the granddaddy of the Tiger Loop. I can't remember why they aren't used much. Firedragon would likely know.
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Thanks for the response Bob.
    I actually did something crazy....download the manual. It apparently relieves pressure on the pump seal when switching from hi fire to lo fire.

    There was an error rendering this rich post.

    Bob Bona_4
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    Interesting! I've not been exposed to much commercial burners. I can see that though
  • OuterCapeOilguy
    OuterCapeOilguy Member Posts: 49
    I've not run into that setup yet. The commercial setups I've worked on are all two-pipe. I'd be inclined to replace that loop with a deaerator.