Buffer tank addition to radiant?
Options
wcs5050
Member Posts: 131
Customer has W-Mc Ultra boiler directly connected to radiant manifold.. with proper pro/sec piping. Would a buffer tank addition increase performance of system?
0
Comments
-
-
Thx for the comments Gordy. Boiler is oversized, but it can be choked way back via reprogramming. I suppose the whole point of the buffer is to fight short cycling in the instance you described.0
-
Exactly. So if you have multiple zones, and those zones are less than min modulation then yes, or combine zones. If boiler is over sized yes. I would not expect huge savings compared to right size boiler, and well thought out zoning, but will extend life of boiler components.0