Proper sized heating unit?
                
                    nydoodles                
                
                    Member Posts: 3                
            
                        
            
                    I'm in the middle of an addition/renovation adding 1500 sq. ft. to my current 1500 (all single floor) in WNY.  I will be removing my forced air unit and replacing with radiant heat throughout.  Addition is 3/4 slab with a 288 sq ft. basement connected to my current full basement.   My contractor has recommended a Peerless Purefire 4 (210,00 B.T.U.) unit.  Seems a wee bit large to me...     I haven't had a heat loss assessment made.                
                0                
            Comments
- 
            A detailed heatloss has to be done or it;s all guesswork.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 - 
            even if you did 50 BTU per square foot you only need 14,400.0
 - 
            Went to loadcalc.net and this estimated a 125,000 BTU requirement.0
 - 
            Never let him in your house again ! Traveled to Plattsburgh in Nov. 14' where the homeowner had a 145,000 BTU boiler , why so big ? Snowmelt ! That boiler is much too large for the house , roughly the same size home as yours after completion .
We had to add an 80 gallon buffer tank to calm the mod con down among other measures to actually melt snow and get ALL the upstairs rooms comfortable .
get a room by room heat loss done by someone or perform it yourself , you'll be amazed .You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38331 - 
            
 - 
            
 - 
            Second, third, fourth... get that heat loss done. The place I care for is over 7,000 square feet, essentially uninsulated, and uses 300,000 BTU on a -10 F day. The boiler is rated at 385,000 BTU. Your 210,000 BTU has to be oversized.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 
Categories
- All Categories
 - 87.2K THE MAIN WALL
 - 3.2K A-C, Heat Pumps & Refrigeration
 - 59 Biomass
 - 427 Carbon Monoxide Awareness
 - 118 Chimneys & Flues
 - 2.1K Domestic Hot Water
 - 5.7K Gas Heating
 - 113 Geothermal
 - 164 Indoor-Air Quality
 - 3.7K Oil Heating
 - 73 Pipe Deterioration
 - 1K Plumbing
 - 6.4K Radiant Heating
 - 393 Solar
 - 15.5K Strictly Steam
 - 3.4K Thermostats and Controls
 - 56 Water Quality
 - 51 Industry Classes
 - 49 Job Opportunities
 - 18 Recall Announcements
 