Proper sized heating unit?
nydoodles
I'm in the middle of an addition/renovation adding 1500 sq. ft. to my current 1500 (all single floor) in WNY. I will be removing my forced air unit and replacing with radiant heat throughout. Addition is 3/4 slab with a 288 sq ft. basement connected to my current full basement. My contractor has recommended a Peerless Purefire 4 (210,00 B.T.U.) unit. Seems a wee bit large to me... I haven't had a heat loss assessment made.
A detailed heatloss has to be done or it;s all guesswork.
3PSI gauge0 -
even if you did 50 BTU per square foot you only need 14,400.0
Went to loadcalc.net and this estimated a 125,000 BTU requirement.0
Never let him in your house again ! Traveled to Plattsburgh in Nov. 14' where the homeowner had a 145,000 BTU boiler , why so big ? Snowmelt ! That boiler is much too large for the house , roughly the same size home as yours after completion .
We had to add an 80 gallon buffer tank to calm the mod con down among other measures to actually melt snow and get ALL the upstairs rooms comfortable .
get a room by room heat loss done by someone or perform it yourself , you'll be amazed .You didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
Rich McGrath 732-581-38331 -
Second, third, fourth... get that heat loss done. The place I care for is over 7,000 square feet, essentially uninsulated, and uses 300,000 BTU on a -10 F day. The boiler is rated at 385,000 BTU. Your 210,000 BTU has to be oversized.Br. Jamie, osb
