Circulator placement
Marz
Marz Member Posts: 90
Hello all. I got a call today from one of our customers. We installed a boiler for this customer back in May. He stated to me that his plumber said that we had installed the circulators in the wrong place. We installed 3 Grundfos circs on the supply after the expansion tank. I know that this is the correct location, but i'm looking to see if anyone has any literature that I can forward to him for peace of mind. Thank you
  • RobG
    RobG Member Posts: 1,844
    edited July 2015
    Tell the customer to come to this site and search "pumping away". And tell them to keep the plumber away from the boiler! The only reason cast iron boilers are shipped with the circ on the return is for shipping purposes. I wish they just packed them loose.
  • Marz
    LOL. that's great! Thank you
  • RobG
    What kind of boiler is it? Some people put the circ on the supply to keep it cooler. The way I look at it is as long as it pumping away from the x-tank and the manufacturer doesn't;t say it's wrong, you're good.
    hot_rod Member Posts: 27,073
    It's this simple, really. Pumping away adds the pumps delta P to the circuit, pumping towards, subtracts it. Under some conditions that will keep the circ in near constant cavitation when you pump at the expansion tank connection.
    Yes you can pump on the return, just move the expansion tank connection there also.
    Leave the air purger on the supply, always.
    RobGZman