Circulator placement
Marz
Member Posts: 90
Hello all. I got a call today from one of our customers. We installed a boiler for this customer back in May. He stated to me that his plumber said that we had installed the circulators in the wrong place. We installed 3 Grundfos circs on the supply after the expansion tank. I know that this is the correct location, but i'm looking to see if anyone has any literature that I can forward to him for peace of mind. Thank you
0
Comments
-
Tell the customer to come to this site and search "pumping away". And tell them to keep the plumber away from the boiler! The only reason cast iron boilers are shipped with the circ on the return is for shipping purposes. I wish they just packed them loose.0
-
LOL. that's great! Thank you0
-
What kind of boiler is it? Some people put the circ on the supply to keep it cooler. The way I look at it is as long as it pumping away from the x-tank and the manufacturer doesn't;t say it's wrong, you're good.0
-
It's this simple, really. Pumping away adds the pumps delta P to the circuit, pumping towards, subtracts it. Under some conditions that will keep the circ in near constant cavitation when you pump at the expansion tank connection.Marz said:Hello all. I got a call today from one of our customers. We installed a boiler for this customer back in May. He stated to me that his plumber said that we had installed the circulators in the wrong place. We installed 3 Grundfos circs on the supply after the expansion tank. I know that this is the correct location, but i'm looking to see if anyone has any literature that I can forward to him for peace of mind. Thank you
Yes you can pump on the return, just move the expansion tank connection there also.
Leave the air purger on the supply, always.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements