Just wrapped up a job on a two-pipe Vapor system. Based on the sideways Illinois radiator traps and express riser / down-feed set up, it looks like a form of Illinois Vapor system. There were no other mechanical devices in the boiler room to give a solid confirmation. Haven't done much other research on it yet.
Main complaints were massive water hammer is portions of the system and uneven heating all around the house. The house is in historic Mendham, NJ, built in the mid 1700's.
We repiped the boiler header (new 5" drop-header), removed an uneccessary condensate pump, added orifice plates to all the radiators, installed a set of new vents on the return and end of main, and put in a 2-stage gas valve and Vaporstat. I also added a drip-trap to the express main for good measure. When I cut out the plug, a few cups of water came out, so that effort feels well spent.
ChrisJ
  • JStar
    JStar Posts: 2,752
    Bonus!
    There was still a pile of unused coal behind the wall to the left of the boiler.
    RobG
    Jamie Hall Posts: 27,826
    Nice job! I still have a pile of coal in my basement... there are things its useful for, now and then.
  • JStar
    JStar Posts: 2,752
    Stocking stuffers?
    Steamhead Posts: 18,907
    Looking good!
    Semi-retired
    RobGvaporvac
  • Yes, what is that coal good for, besides christmastime for bad children?--NBC
  • SWEI
    SWEI Posts: 7,342
    Gorton clearly owes you a thank-you note :smiley:
    RobGJUGHNE
  • BobC
    BobC Posts: 5,576
    Perhaps a few lumps of coal for each of the burgeoning group of presidential hopefuls?
    Bob
    3PSI gauge
  • JUGHNE
    JUGHNE Posts: 11,636
    So are there 4 #2 vents on the end of steam main return drip into the wet return........and are there 4 #2 on the dry return going into the wet return??
    Did you feel that venting all the air thru the rad inlet orifices, rather than the discharge traps (which I assume are empty) would be slower than original design?
    Do your dry returns, which I assume never see steam with the orifice system, get hot enough to close the #2's?
    How did you size the orifices, EDR X 80% maybe, but how did you select the pressure?
    I better quit before it gets to 20 questions.
    Thanks