Exterior Chimney
Jlamb
Member Posts: 14
in Gas Heating
Does anyone know the correct definition of an "exterior' chimney?
And when you line an exterior chimney with a stainless steel liner, is that not considered insulated?
One wall of chimney exposed to outdoors. It's not insulated it's lined.0
It is common for an outside lined chimney to condense. This can be exacerbated by oversized equipment. Exterior chimneys are just tough to use...confidently.0
Hmmm so technically speaking all chimneys with the rear exposed are not suitable for gas equipment?
There are a lot of gas conversions in Maine taking place and I can see this being a problem.
Especially because more than half of all chimneys have one side exposed.0 -
Actually, the problem is that masonry chimneys have absolutely no place in venting todays equipment, oil or gas. masonry chimneys are typically oversized heat sink. They are like the adobe homes in the southwest. Absorb heat all day and give it up to the interior at night...except that they never give it up to a positive outcome. They just suck the heat and energy out of the flue gases and systems suffer.Jlamb said:Hmmm so technically speaking all chimneys with the rear exposed are not suitable for gas equipment?
The gas industry, which as public utilities was highly regulated, went through this in '92 when the energy codes required a minimum of 78%. The old draft hood equipped furnaces were in the low 60% range. This was a profound difference and took subsequent issues of '54 to get tighter and tighter in recognition of the physics of combustion and dew point problems. The oil industry which isn't regulated in the same way has been able to "avoid", intentionally, relining issues, although the physics of combustion are the same. For reference check out Appendix E in 31.
Net/net, the real issue is that we are venting 21st century appliances with 11th century technology when we use any masonry chimney. In todays world with todays equipment masonry chimneys are excellent architectural devices, but terrible mechanical devices!2 -
The solution if possible is to run "B" vent up through the existing chimney using the chimney as a chase. The code allows this and the Handbook for NFPA 54 shows a picture of this being done.0
Great! Thanks for the help!0
Tim, correct me if I'm wrong but if you use a liner, and install it in a existing tile lined chimney is then falls under the B vent sizing charts.
No?0 -
Most liners are actually 20% less capacity than "B" Vent. I suggest using the charts from the manufacturer of the liner.0
- 76 Pipe Deterioration