vapor steam
I installed a steam boiler on a vapor system. I installed a vaporstat, and set at 2oz on 8oz off. The gas valve cycles on for 45 seconds then off for 45 seconds. Is that ok, and if not how do I lengthen the run time?
    Steamhead Posts: 18,834
    Does it do this beginning at a cold start, or only after the system has completely heated up?
    What boiler did you use?
    How much radiation is there?
    What type of Vapor system is it (Dunham, Hoffman, Tudor, Webster etc.)?
  • al3
    al3 Posts: 5
    Thanks steamhead, ,Its a Utica J 400. I'm not sure of the system name. A great steam guy in my area showed it to me years ago. The rads use regular rad 90 with a disc with one or two holes in them to let out condensate and air. There is 810 square ft radiation in the house so I sized the boiler to the radiation. the system was already hot when I swapped the pressuretrol for vaporstat , so it really didn't have to come up from cold start
    That's probably an early Trane system. See chapter 15 of "The Lost Art of Steam Heating" for details.
    How does the air get out of the dry returns?
  • Abracadabra
    Abracadabra Posts: 1,949
    What is a Utica J 400? Do you mean a Utica JE400? 970sq.ft steam?
    Do you have a low pressure gauge installed to verify that it's the vaporstat cycling the boiler on/off at your setpoints?
  • al3
    al3 Posts: 5
    there is a Hoffman condensate pump, air is vented through the tank vent tapping. there is a 6 inch deep 1 1/4 copper trap before the tank. I think that needs to be taken out and a f&t trap installed. and yes JE 400
    Jamie Hall Posts: 27,743
    45 seconds on, 45 seconds off is almost certainly NOT the vapourstat, although you can easily check that by jumping across the vapourstat terminals. Sounds much more like a problem with the burner controls.
  • Abracadabra
    edited February 2015
    That's part of your problem. The water trap is blocking the air that's trying to escape.
    Do NOT install an F&T trap there. It will really slow down the returning condensate. The pipe should slope down to the tank inlet with nothing to block the air flow.
    If steam reaches the tank, the pressure is probably too high. Crank it DOWN!
    The real question is- do you really need that tank and pump? I'd bet you don't.