vapor steam
al3
Member Posts: 5
I installed a steam boiler on a vapor system. I installed a vaporstat, and set at 2oz on 8oz off. The gas valve cycles on for 45 seconds then off for 45 seconds. Is that ok, and if not how do I lengthen the run time?
0
Comments
-
Does it do this beginning at a cold start, or only after the system has completely heated up?
What boiler did you use?
How much radiation is there?
What type of Vapor system is it (Dunham, Hoffman, Tudor, Webster etc.)?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks steamhead, ,Its a Utica J 400. I'm not sure of the system name. A great steam guy in my area showed it to me years ago. The rads use regular rad 90 with a disc with one or two holes in them to let out condensate and air. There is 810 square ft radiation in the house so I sized the boiler to the radiation. the system was already hot when I swapped the pressuretrol for vaporstat , so it really didn't have to come up from cold start0
-
That's probably an early Trane system. See chapter 15 of "The Lost Art of Steam Heating" for details.
How does the air get out of the dry returns?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
What is a Utica J 400? Do you mean a Utica JE400? 970sq.ft steam?
Do you have a low pressure gauge installed to verify that it's the vaporstat cycling the boiler on/off at your setpoints?0 -
there is a Hoffman condensate pump, air is vented through the tank vent tapping. there is a 6 inch deep 1 1/4 copper trap before the tank. I think that needs to be taken out and a f&t trap installed. and yes JE 4000
-
45 seconds on, 45 seconds off is almost certainly NOT the vapourstat, although you can easily check that by jumping across the vapourstat terminals. Sounds much more like a problem with the burner controls.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Abracadabra said:
Do you have a low pressure gauge installed to verify that it's the vaporstat cycling the boiler on/off at your setpoints?0 -
That's part of your problem. The water trap is blocking the air that's trying to escape.al3 said:there is a Hoffman condensate pump, air is vented through the tank vent tapping. there is a 6 inch deep 1 1/4 copper trap before the tank. I think that needs to be taken out and a f&t trap installed. and yes JE 400
Do NOT install an F&T trap there. It will really slow down the returning condensate. The pipe should slope down to the tank inlet with nothing to block the air flow.
If steam reaches the tank, the pressure is probably too high. Crank it DOWN!
The real question is- do you really need that tank and pump? I'd bet you don't.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements