3 zone control panel went out
JStreet24
Member Posts: 5
in Gas Heating
Woke up this morning and noticed that all three thermostats were out so I replaced the batteries then went upstairs to the furnace and noticed that the lights on the control box were out. What can I do to fix this issue. The furnace continues to blow air but if feels cool.
We'll is it losing power? Way way to many scenarios.. But have to start looking at power.0
Does the zone controller power/charge the thermostats (or batteries in them)? I would start by checking if the zone controller is getting power (assuming line, 110V) and checking if it has any fuses inside.
Need more info...0 -
Yes, the zone controller powers the thermostats. all 3 thermostats have battery compartments bdidn't put batteries in them because I'm guessing that there isn't a need.0
Make sure there is power going to that control panel, I don't know if its 120 vac or 24vac but it needs a power source. Do you have a meter to check it?
If there is power, make sure all the connections are tight, it only takes one loose screw or connector.
3PSI gauge0 -
No I don't have a meter to check it but all connections seem tight. It was working perfectly for three years until it went out yesterday. I check to see if a fuse blew but can't find a fuse on it. I attached a picture of the unit if that helps.0
It is one zone with 3 electronic dampers which controls the 3 thermostats not 3 zones btw.0
It doesn't look like its powered of the mains (110V), so probably by 24VAC off a separate transformer or maybe a controller/furnace itself...
If you don't have a meter to measure voltage, it'll be much harder to troubleshoot. Harbor Freight has cheapo ones for like $5. While I wouldn't count on it for giving me very accurate values, it should be sufficient to tell you if there is voltage present.
Here you go: http://www.zonexproducts.com/us/products/digitract-3/digitract-3-wiring-schematics/0 -
You should have 24VAC across the red and blue wire (circled in red):
Powers comes from HVAC unit0 -
Did you recently change your air filter. If so you may not have the furnace door on properly. Or the switch is off to the furnace.0
Proper way to install a zone panel is with a separate transformer to power the panel. The transformer in the furnace is rarely of sufficient capacity (va) to do it. We have that same panel in our office. I'm believing without crawling up there that the 2 upper right terminals are the 24v to run the panel0
It appears, as others have noted, that the zone panel may be powered from the furnace's transformer which may not be sufficient to carry everything. There may be a fuse for that on or around the furnace's control board.
Looking at the pic of the zone panel, it appears the bottom terminal strip goes to the equipment. If that is so, temporarily jumper the "R" and "W" terminals and see if the furnace comes on. If it does, then the zone panel is probably not powered from the furnace. If it doesn't, then it probably is and that's where the problem is.
As noted, make sure the door is on the furnace tightly or it won't be powered. Also, check switches and circuit breakers.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0