How to loosen setscrews on scaleplate to recalibrate pressuretrol
Pressuretrol not turning boiler off at 5 psi when set cut in 0.5 psi and cut out 1.5 psi.
Seems not functioning observed pressure up to 5psi I have to turn boiler off myself
  • BobC
    BobC Posts: 5,577
    Have you checked the pigtail is not blocked? While the pressuretrol is off check the little hole at the base of it's brass fitting to make sure that little hole is clear.
    Also make sure the spring has not decoupled from the lever.
    Bob
    3PSI gauge
    rrwitherspoon
    Jamie Hall Posts: 27,922
    That's more than a calibration error. Follow Bob's advice -- and check the pigtail and where it goes into boiler, too.
    Might make sure that it is wired properly, if that doesn't hep...
  • The pigtail is clear.The little hole on bottom of pressuretrol is patent. How do you make sure not decoupled from lever?
  • Wired as it always was when functioning .Pink wire at top.
  • Ok i will try when i get home
  • Everything is engaged. No misaligned ferrules
    or levers. Should the contact fork wires of pressuretrol be placed between metal nut and screw? Like a sandwich ? Maybe that is the problem.
  • BobC
    BobC Posts: 5,577
    As long as the wire is under the head of the screw or one of it's washers, the contact should be solid. Have you had a chance to turn off the power while the boiler is firing and delivering 5PSI, remove one wire, and see if the boiler starts up when you reapply power? If the boiler. If it does not it indicates something is wrong with the pressuretrol.
    There is always the possibility that the gauge is not working right. At 5PSI I would expect the vents would be hissing a bit loud, any signs of increased noise?
    Bob
    3PSI gauge
  • Yes, at 5 psi the last radiator supply valve hisses and a leak appears that otherwise you would not even detect
  • I will get vapostat and low pressure gauge installed
  • Shall I install vaporstat just like pressuretrol.
    I noticed there 3 wires instead of 2
  • SWEI
    SWEI Posts: 7,342
    SPDT terminals. You want break on rise.
  • Does one use all 3 terminals?
  • No. You want to connect to the two terminals R and B that "break on rise." Don't buy a two terminal vaporstat.
  • I hope instructions come with vaporstat for wire connections
    L408 1017 model number