Condensate Return Line Cleanout System: looking for recommendations
KevinK
Member Posts: 67
System details: one pipe steam; residential; 150,000 btu boiler.
My 85 year old iron condensate return lines had to be replaced due to corrosion and sediment build-up. This was done 4 years ago; the new lines are copper. I am wondering whether I should add a cleanout system. I am looking for nput/recommendations.
The CR lines consist of two legs of approximately 50 ft each. I am assuming that I would need something like a ball valve at each elbow where the CR vertical drop “elbows” to horizontal. (Maybe on a wye on the drop?) And then another ball valve at the cleanout where the CR line meets the near-boiler plumbing. If I had garden hose fittings at each of these three locations, I could use a garden hose, first from one side and then the other, to wash out the sediment. The discharge could be conveyed to my basement floor drain via a second garden hose. If I did this once per year, I’m thinking that I could maintain clean CR lines for generations. So, my basic questions are:
1. Is a CR cleanout system recommended?
2. Is there a standard approach to this/what are the recommended “details?” E.g., type and location of inlet and outlet valves; mechanism for conveying the discharge to floor drain.
3. Are there issues that I haven’t thought of or am unaware of? I am asking this in part because it seems like such a no-brainer, and yet I haven’t seen this mentioned anywhere.
Thanks.
Thanks.
One-pipe steam. NG fired. 2100 sq ft heated space.
Utica Boiler PEG150C (150,000 Btu/hr Input) connected to 491 sq ft of radiation. Operating press 0.5 psi.
A cleanout arrangement
is a good idea -- although you may find that once a year is more than enough. Surprising how clean steam is...
If it were mine to play with, though, I'd have a ball valve where the lines meet the boiler piping, so you could isolate the boiler from the returns (not a bad idea anyway -- that way, with a king valve on the connection from the header to the house system you can completely isolate the boiler if you even need to raise the pressure on it slightly). But I wouldn't bother with big valves on the rest of the return system -- they're expensive. Instead, have drain cocks (you need them anyway) and use T's with a threaded plug. Just close the main valve, open the drain cocks, undo the plugs and blast away with your hose...Br. Jamie, osb
Thanks
Thanks for your input. The CR lines are 1-1/4” copper. Through my local htg equip supplier, I found the Webstone 3-way ball valve that has a capped hose connection:
http://www.webstonevalves.com/default.aspx?page=item+detail&itemcode=50614W&catlist=24
I plan to install these on the two CR drops.One-pipe steam. NG fired. 2100 sq ft heated space.
Utica Boiler PEG150C (150,000 Btu/hr Input) connected to 491 sq ft of radiation. Operating press 0.5 psi.0 -
Ball Drains rock
One of our favorite fittings. Buy them by the box.0